And to bring my side of this thread to a close.

The landlord has had another FRA done and the system has been put down as LD2 D1 so he's going for a wireless system...
 
Yes it will still need a supply, but a Grade D1 system can be wired to local lighting circuits and radio interlinked. And as they are self contained they will not need wiring in FP.
 
  • Agree
Reactions: Strima
Ah, OK.

I had assumed it was like Flexishield and the foil shield would take out the RCD/OCPD if penetrated by a nail, etc.

Thanks for this info westwood10. I did not realise that FP200 is not suitable for this application. Following on from your post, I did a little research. I think it has to do with the construction of the foil shield, in that it is not capable of carrying a large fault current for long enough to operate the OCPD. Every day's a school day...

In many systems if FP200 is employed it uses the foil as a shield from interference and if it is a monitored addressable system in use then the foil and 'earth' core is effectively isolated from common supply earth and is separately monitored by the panel, you can easily identify where this is in place as the panel usually has separate terminal inputs for the 'earth' core and any device will be clear on connecting up the devices that the 'earth' core is not fitted to any common installation earth.

@pc1966
I assume you are simply talking domestic 230v mains linked systems here which seldom use FP200, almost all systems using FP200 are monitored and the voltage down these cables is <30v DC, shorting the cable out will either pop a F/A panel glass fuse and/or the panel will actually isolate that particular zone and flag a fault warning.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Fire Alarm Circuit RCD Protection TT System
Prefix
N/A
Forum
Commercial Electrical Advice
Start date
Last reply date
Replies
24

Advert

Thread statistics

Created
Strima,
Last reply from
Darkwood,
Replies
24
Views
5,988

Advert