And to bring my side of this thread to a close.

The landlord has had another FRA done and the system has been put down as LD2 D1 so he's going for a wireless system...
 
Yes it will still need a supply, but a Grade D1 system can be wired to local lighting circuits and radio interlinked. And as they are self contained they will not need wiring in FP.
 
It will still need a supply!
Fed from a local lighting circuit which is acceptable.

I'm only getting involved with wiring the bases etc, another company is being paid to design and commission the system.
 
Ah, OK.

I had assumed it was like Flexishield and the foil shield would take out the RCD/OCPD if penetrated by a nail, etc.

Thanks for this info westwood10. I did not realise that FP200 is not suitable for this application. Following on from your post, I did a little research. I think it has to do with the construction of the foil shield, in that it is not capable of carrying a large fault current for long enough to operate the OCPD. Every day's a school day...

In many systems if FP200 is employed it uses the foil as a shield from interference and if it is a monitored addressable system in use then the foil and 'earth' core is effectively isolated from common supply earth and is separately monitored by the panel, you can easily identify where this is in place as the panel usually has separate terminal inputs for the 'earth' core and any device will be clear on connecting up the devices that the 'earth' core is not fitted to any common installation earth.

@pc1966
I assume you are simply talking domestic 230v mains linked systems here which seldom use FP200, almost all systems using FP200 are monitored and the voltage down these cables is <30v DC, shorting the cable out will either pop a F/A panel glass fuse and/or the panel will actually isolate that particular zone and flag a fault warning.
 

Reply to Fire Alarm Circuit RCD Protection TT System in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
TT system, existing three phase fuse board recently installed by another spark which only has single phase circuits terminated into individual...
Replies
15
Views
4K
On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
959
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
1K
Over the last few days, I have stumbled across a number of threads that seem to point to a prevalent misunderstanding. Either that, or I have been...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock