Hi All
I've been asked to tender for a fixed wire test for a hotel group here in Ireland.
They sent me documentation to read through before I tender.
The hotel group is UK based so therefore the regulations would also be British standard rather than the Irish standard I work to.
I would assume it's pretty similar anyway but if you wouldn't mind helping me with a few questions I have?
My question first is about the Earth Loop Impedance.This is part of what they sent me.
12.1 Earthloop impedance
Earth loop impedance tests to be carried out at locations indicated below: -
(a) At the origin and at each distribution board.
My reading of that is I don't have to do an earth loop test on every lighting circuit? There is no mention of it in the above,all they mention are sockets. Is this the norm in the UK? I would have always done an earth loop test on every circuit.
Here then then mention Only a sample of lighting circuits need to be continuity tested.I presume they mean the R1+R2 test here?
11.1 Continuity testing of protective conductors to include: -
(a) Earthing Conductors.
(b) Main Equipotential Bonding Conductors.
(c) Supplementary Bonding Conductors.
(d) All circuit protective conductors (sample lighting circuits).
(e) Exposed conductive parts on installed machinery/fixed equipment.
Also,they only request 20% of all circuits need to be Insulation resistance tested. Is this also the norm for a fixed wire test in the UK?
Really sorry for the long post,any advice or help would be appreciated,especially about the earth loop testing on lighting circuits.
I've been asked to tender for a fixed wire test for a hotel group here in Ireland.
They sent me documentation to read through before I tender.
The hotel group is UK based so therefore the regulations would also be British standard rather than the Irish standard I work to.
I would assume it's pretty similar anyway but if you wouldn't mind helping me with a few questions I have?
My question first is about the Earth Loop Impedance.This is part of what they sent me.
12.1 Earthloop impedance
Earth loop impedance tests to be carried out at locations indicated below: -
(a) At the origin and at each distribution board.
- All socket outlets.
- Any location, which is exposed to exceptional damage or deterioration or represents a special hazard.
- Whilst 100% of fixed equipment is tested for Earth Continuity, a further 10% sample will be checked for Earth Loop Impedance.
My reading of that is I don't have to do an earth loop test on every lighting circuit? There is no mention of it in the above,all they mention are sockets. Is this the norm in the UK? I would have always done an earth loop test on every circuit.
Here then then mention Only a sample of lighting circuits need to be continuity tested.I presume they mean the R1+R2 test here?
11.1 Continuity testing of protective conductors to include: -
(a) Earthing Conductors.
(b) Main Equipotential Bonding Conductors.
(c) Supplementary Bonding Conductors.
(d) All circuit protective conductors (sample lighting circuits).
(e) Exposed conductive parts on installed machinery/fixed equipment.
Also,they only request 20% of all circuits need to be Insulation resistance tested. Is this also the norm for a fixed wire test in the UK?
Really sorry for the long post,any advice or help would be appreciated,especially about the earth loop testing on lighting circuits.