S

sparks72

Hi

I hope this makes sense.

Went to look at a job a few days ago, did a quick test on the incomer of a 3 phase supply TNC-S system (seperate from the main consumer board) got a Ze of 0.19, all good, went to test the seperate consumer board & got a Ze of 0.33 & a Zs at a few RCBO protected sockets, the max being 1.80!
Went back a few days later & did the same test, Ze at incomer was 0.19 but Ze at property had shot up to 3.88!! did an IR test on mains cable & all good.
I added a new 25 mm earth conductor to the main incomer & the Ze at the property lowered to 0.22 & Ze at the RCBO sockets was a max of 0.68!
went back today & the Ze at the property board had gone up again to 0.31 & the Zs at the RCBO protected sockets had risen to a max of 1.77!
Had the LEB look into their side of the supply & got the all clear.
The cable from the main incomer to the property is a 25mm 2 core SWA using the steel wire as the earthing, the run from incomer to property is around 50 metres.
I think their is a split in the SWA sheathing. probable damage when installed 10 years ago (no certs)
has anyone else come across this & if so what was the problem. :confused:

Thanks.
 
Last edited by a moderator:
i agree with you on the split sheath/ corroded armour. this is the reason that i never use the armour as CPC when cable is run underground.
I worked on a job in wolverhampton city centre, and when i carried out site survey to size submains to our panels the ZE was 0.08 (winter). When i tested the job at the commisioning stage (summer) the ZE was 0.56. the LEB weren't interested. they said that fluctuation due to water levels is normal. this was a TNC-S system
 
i agree with you on the split sheath/ corroded armour. this is the reason that i never use the armour as CPC when cable is run underground.
I worked on a job in wolverhampton city centre, and when i carried out site survey to size submains to our panels the ZE was 0.08 (winter). When i tested the job at the commisioning stage (summer) the ZE was 0.56. the LEB weren't interested. they said that fluctuation due to water levels is normal. this was a TNC-S system


Cheers johnboy.
The company that did the initial installation is well known for "cutting corners".
I'm scratching my head as to what to do really, told the customer what might have happened but they
don't want any excavation done.
Could turn it into a TT System but same thing again, customer dosn't want all the hassle as they've recently moved in & had to endure a barrage of bad workmanship that has cost them a small fortune.
I've warned them of the danger without the woman bursting into tears (again)
Now the big question, on a periodic......satisfactory with a code 2 or un-satisfactory ?
I would say unsatisfactory personally but I can't endure more tears from the customer!! :(
 
could you not bring down the ZS of the ring final circuit with supplementary bonding? i would also run a seperate earth next to the submain. If its 16mm2 or over, it can be buried without protection. This should bring your readings down.
 
could you not bring down the ZS of the ring final circuit with supplementary bonding? i would also run a seperate earth next to the submain. If its 16mm2 or over, it can be buried without protection. This should bring your readings down.

Their are 3 ringmains in the house, I have no access anywhere really as the house has water fed underfloor heating throughout (chipboard on top of pipes)
I would run a seperate earth next to the submain but they have a stone courtyard that the cable runs underneath & they don't want it digging up, to dig it up (excavation quote) would cost at least £5k! :eek:
 
Just slapped myself!

Apparently I can install an earth electrode on a TNS system ( PME) for additional protection, the IEE recommend it.
 
Last edited by a moderator:

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Fluctuating voltage!
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
9
Unsolved
--

Advert

Thread statistics

Created
sparks72,
Last reply from
sparks72,
Replies
9
Views
2,281

Advert

Back
Top