Any help would by greatly appreciated as i have tried everything i possibly can. Heres some info on the situation, installed some spike lights a year or so ago. Couple of weeks ago they tripped so went round and found one of the wiska boxes to have been damage and water had gotten in. So replaced the box and sealed it with gel all was well for a little while then it started going again. So i have tried; Testing the RCD all good reading, Changing all the led bulbs incase one was faulty, replaced a couple of fittings that looked a little worn may have been hit by the gardener, Tested the armoured throughout the circuit and checked all joint boxes and lights for any water and nothing. The only strange thing i cant under is when i remove the LED's form the circuit and do an insulation test with the fittings in i get a down reading but they are only knightsbridge mains GU10 spike lights but the cable is brand new. Now they work for a couple of hours then trip? why would this be and not straight away...

Any help would be amazing.
Thanks in advance
Ryan
 
Thinking about the two hours then the RCD trips suggest to me that something is heating up slowly and gets to a point that causes the RCD fault. I was thinking of water but heat makes more sense, maybe???
 
Corrosion on the connections that were wet perhaps? This could potentially give them a high resistance but not high enough to actually stop everything working straight off. The extra build up of heat over time could be causing your fault which disappears again when the cct is deenergised.
 
The Knightsbridge spike lights are terrible I fitted some last year and 3 out of 12 filled with water after a couple of weeks.
I replaced them with Ansell ones, far superior product.
 
Thinking about the two hours then the RCD trips suggest to me that something is heating up slowly and gets to a point that causes the RCD fault. I was thinking of water but heat makes more sense, maybe???
This was my thought as ive tested and changed all the bulbs possibly one of the connections could be slightly loose but they are all gel filled......
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
Hertfordshire
Business Name
RAS Electrics

Thread Information

Title
Garden lighting issue
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
18
Unsolved
--

Advert

Thread statistics

Created
Ryans94,
Last reply from
weevilward,
Replies
18
Views
3,675

Advert

Back
Top