yes i would do this on a totally different circuit, would do cable calcs for appliances also to make sure it is suitable.
 
Cool, I'll look in to this then.

My problem is I don't know what is accepted practice with domestic...!
 
I assumed the fusing down was implied. To be honest ive only ever done the grid switching for below counter oitlets once and found it to be alot harder work than the usual fused isolaters above worktop in line with an outlet below the worktop. And i used click grid switches which come marked up for appliances and they do the fuse carrier modules to allow for fusing down
 
We do work for barratts homes, moriss homes, redrow and a load of other large builders and we always put the grid switches on a seperate 20 amp supply. If there is a utility we will also run a seperate one to here also.
 
what could be easier a supply to a grid, link your lives and then terminate into an un switched socket, simple all switching done in the same place!
 
what could be easier a supply to a grid, link your lives and then terminate into an un switched socket, simple all switching done in the same place!

This now makes sense, ill have to have a look at the back of one at some point...

A separate 20a radial sounds good to me! At this rate ill have two or three fuseboards haha
 
You wire a 20a double pole to each under counter socket for each appliance off the ring, marked up on switch what they're for, i don't see why people on this thread have a problem with this? I also wouldn't go cutting the plugs off appliances to wire them straight in as it will invalidate the warranty
 
Just a quick note. Just moved into a new build house. Dishwasher, washing machine and fridge on 20A dp grid switches with spurs behind the said appliances. Oh, and the grids are off the kitchen ring.
 
I just don't understand why Fused Connection Units are there for the appliances under the units to connect to, whats wrong with an unswitched single socket and the appliances with plug tops on them, surely cutting off plug tops and connecting to FCUs will void the warrenty on appliances? Just my view, however headache now appearing :6:
 
You wire a 20a double pole to each under counter socket for each appliance off the ring, marked up on switch what they're for, i don't see why people on this thread have a problem with this? I also wouldn't go cutting the plugs off appliances to wire them straight in as it will invalidate the warranty

IT WILL NOT INVALIDATE ANY WARRANTY, ...Jesus how many more times!!!
 
First. I'll warn you, I'm half cut, so if admin take the huff, then oh well, I'll deal with that tomorrow !
Right, tell me, the posters above me, are any of you sparks ? Running a spur, through a 20a DP switch UNFUSED ! I've done something similar to this once, when I was an apprentice, even then I had the (half) sense to use a 32a dp switch !
Next, running a 6mm for a grid bank, again with no fuses, either means a low load with about a 150m run, or you haven't a clue ! If it's the second one, do yourself a favour, get yourself a QUALIFIED sparkie in !

Well, i consider myself as suitably qualified, so i'll answer your post accordingly...lol!!

What's different about taking a spur off a ring circuit to a single/double socket to using an unfused 20A grid switch?? Also none of these appliances would be subject to overload conditions.

Using two 4mm and certainly two 6mm into a multi grid switch arrangement is a non-starter as far as i'm concerned, just not enough space and switch terminals too small to safely accommodate these cable sizes.

I'm not a lover of this grid switch system, though i do see it has it's uses. I prefer to see switched FCU above worktop and an unfused, unswitched outlet below.
 
IT WILL NOT INVALIDATE ANY WARRANTY, ...Jesus how many more times!!!
IT DOES AND IT WILL!! I've had first hand experience of this by chopping a moulded plug off a boiler, wiring it into an fcu and then when it broke it wasn't covered under warranty cos the plug was cut off!!!
 