Hi guys
Does anyone know if the old Hager boards with the 1361 fuses will take a RCBO and if so what type ?
I have found Hager RCBOs but not sure if they are compatible.
Thanks to any replies in advance.
 
Do you mean the type of CU that looks just like a 'new' CU, but instead of CB's inside, it is BS1361 cartridge fuses, in bodies with the same shape as a CB?

If so, then yes, a Hager RCBO will fit in, but it is a tight fit at the top with the other cables there.
 
Hager Rcbos you require should be 32A/30mA = ADN132, 20A/30mA = ADN120, 16/30mA=ADN116 and the 6A/30mA = ADN106. As previous poster has said, tight to fit at top end but will go if distribution board not too jam packed.
 