Today we got our Hager meter kit for one of their 125A TPN boards. It has a little DIN rail fuse holder as the meter is powered right off the incoming isolator/RCD/etc without any MCB for protection (so the meter can't be switched off without everything going off, presumably so you don't cheat on any internal billing but that means).

So I opened it up to look at the fuses and was rather shocked to see a 0.5A glass LRC fuse! You know, the sort with a breaking capacity of 35A at 250V AC! This is off a 400V TPN board that could have a 10kA fault current at that point FFS!

Even replacing the fuse with a 20x5mm HRC fuse is only good to 1.5kA fault rating. What were the product designers thinking?!
 
Type-tested assembly...the fuse shatters but the box keeps the debris contained?
The meter protects the fuse?
Design specified HRC but stores had run out?
Counterfeit switchgear, meter module actually just contains sawdust?

Dunno, sounds carp anyway.
 
  • Funny
Reactions: DPG
LOL it would probably all arc together across the fuse holders if there was a serous fault in the meter module, you could test it out to see what happens? Slydlok FTW!
 
On a similar theme, one well known gas boiler (cant remember which) used to have a fuse on both the line and neutral incoming connections. Could never work out why they thought that was a good idea.
 
. Could never work out why they thought that was a good idea.
..Only qualified should access ..
--who occasionally get polarity wrong ! anyway .--
(external power getting switched to neutral ?)
 
On a similar theme, one well known gas boiler (cant remember which) used to have a fuse on both the line and neutral incoming connections. Could never work out why they thought that was a good idea.

Probably designed for another EU country where it is a requirement and they didn't get the UK variant right.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

pc1966

Esteemed
Arms
Supporter
Joined
Location
Dundee
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Enthusiast (Unqualified Hobbyist etc)

Thread Information

Title
Hager meter kit fusing stupidity
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
6

Advert

Thread statistics

Created
pc1966,
Last reply from
davesparks,
Replies
6
Views
1,449

Advert