just trying to borrow a IR tester.

It is a complete head scratcher, he also said aswell when he canged a bulb in the downlight it didnt come on at first and he wiggled the cable and it came on so I wonder if hes pulled a connection out in junction box in the floor
so is said joint box accessable?....
wants to be really doesn`t it....
 
well, that's the first place to look then. see my last offering.post 13.
 
it just confuse me why when the shower and kitchen lights are on together ( powerd by seperate RCDS) they trip when i disconnect shower kitchen lights come on, and when i disconnect kitchen lights the shower etc works fine
 
has the customer been diy-ing? its a line-earth fault for sure, maybe trapped/penetrated cable. Is there a bathroom above the kitchen tat may have leaked/ hot water pipes in ceiling ?
 
reason i suggested what i did is that i've come across a similar fault. N/E short on RFC fed from RCD2. RCD2 will not trip, even with the test button, but RCD1 trips. there are no crossed neutrals and no loose connections.
 
thanks for advice everybody

Telectrix:

your opinion does sound the most likely as I just spoke to another spark and he said he had a similar fault which was effecting both RCDS and it was a neutral earth fault

Thanks again for help guys hopefully get it sorted panic over for now :)
 
hello there i thought i would tell you the result. I tested the whole lighting circuit for kitchen and found one of the lights had gone down n & e so not so bad in the end thanks for advice
 