Rip it all out, move the pool thingy closer to the house and use a continous piece of external grade T&E. If you cant get the right thickness double it up in parallel to make a nice loop. Just make sure you tie wrap it together. Problem solved, especially if you sack the RCD protection idea!

Can you elaborate on that cable type please.
 
Guitarist 6mm 3 core SWA for 34 metres, terminated into 6mm T&E with additional 10mm earth over 1 metre at both ends from SWA into CU and final hot tub internal connections.
 
Why additional CPC, NOT EARTH!
It cannot be an EARTH, FFS.
How is the FT&CPC run?
Is the run compliant with BS7671 & suitable for the cable type according to BS7671 & the cable manufacturers requirements?
 
Could it be where you have brought the conductors through the gland, separated them by bending them, and the live is pushing hard enough against the gland; causing a low reading?
I've had similar faults to this before
 
Can you elaborate on that cable type please.

Its the nice grey coloured stuff that looks flat. Theres even a piece of shiny wire in the middle of it that you dont have to strip anything off when you use it. You can buy it at B&Q, sometimes for 10% off and even more if you go on OAP day!!
 
External Grade T&E

By way of a disclaimer I disassociate any comments made purportedly by me about “External Grade T&E” on this forum. I can only assume my account was 'frapped' for the few minutes it took me to get another can from the fridge.

Under no circumstances will I accept any comeback from anyone designing circuits using external grade T&E, quoting the requirement for external grade T&E on EICRs or demanding B&Q supply them a few reels at discounted prices on OAP days.

You assistance in this matter is much appreciated.

p.s. I still have a few unused reels at a substantial discount if anyone wants to PM me for details …..
 
By way of a disclaimer I disassociate any comments made purportedly by me about “External Grade T&E” on this forum. I can only assume my account was 'frapped' for the few minutes it took me to get another can from the fridge.

Under no circumstances will I accept any comeback from anyone designing circuits using external grade T&E, quoting the requirement for external grade T&E on EICRs or demanding B&Q supply them a few reels at discounted prices on OAP days.

You assistance in this matter is much appreciated.

p.s. I still have a few unused reels at a substantial discount if anyone wants to PM me for details …..


Cracked me up!
 
Guitarist 6mm 3 core SWA for 34 metres, terminated into 6mm T&E with additional 10mm earth over 1 metre at both ends from SWA into CU and final hot tub internal connections.

Thanks. Just wondered what you had meant by "External grade T&E". Thought I was missing out on something ;)
 