I’m after some advice please. I’m on a job where there’s a junction box with ring main wired in singles through 50x50 galv trunking. I need to break into this ring for my additional sockets but need to identify which of the cables are incoming and outgoing ones!? I can’t follow cable in trunking as it’s butt up against roof and can’t get my fingers in and cables also tangled round others in there. What’s best method to find out which cables are incoming and outgoing circuits?

Thanks
 
If everything can be made dead, if you can inject a decent current in one end and back (low voltage transformer like the train set ones with an adjustment), then you can use a current clamp meter to identify the cores carrying current.

Lot of a faff - usually easiest to pull cables back and forth with an able assistant
 
Normally I'd identify a set of 3 at the CU, break the ring (safely) at furthest point, connect a load, only connect up one set of 3 at CU, and use a clamp meter to identify the L and N showing current.
But I did note that you said you can't get fingers in, so probably no room for a clamp meter either. It sounds like inserting joints is going to be very difficult too even if you find the right cables.

Can you instead disconnect at the next nearest socket, one colour at a time, hook and tape new cables to the ones you disconnected, and pull each in turn at the joint box until one moves, and pull a new length through - then you'd also have some slack to work with for your new connections?
 
There's umpteen ways of doing it with an MFT or multimeter. Probably the best as it doesn't involve opening any other fittings:
1. Isolate circuit, separate conductors at JB, connect one L to one N, leave the other two floating. Test resistance at a number of sockets. If the readings vary progressively the joined L & N are from the same leg of the ring, if they are all similar, the L & N are from opposite legs of the ring.
 
There's umpteen ways of doing it with an MFT or multimeter. Probably the best as it doesn't involve opening any other fittings:
1. Isolate circuit, separate conductors at JB, connect one L to one N, leave the other two floating. Test resistance at a number of sockets. If the readings vary progressively the joined L & N are from the same leg of the ring, if they are all similar, the L & N are from opposite legs of the ring.
I would welcome an article on the different methods of this sort of thing, same with belling out, I know it's a 'simple' thing but it's one I struggle to get my head around ?
 
I would welcome an article on the different methods of this sort of thing, same with belling out, I know it's a 'simple' thing but it's one I struggle to get my head around ?
A variation on the method above is useful for finding out the route of a ring circuit. When ring is not continuous I do this. Both ends out at CU and join two conductors on the same leg one end. Take resistance readings at each socket. If ring is complete then ring circuit route is highest to lowest, lowest being closest to the joined end, highest being closest to the open end. (Spurs can slightly confuse this)
If there’s a break then the last socket with a reading and the first without is where to start.
If IR tests fail I sometimes do this to find the middle to decide where to start breaking it down.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Lincoln

Thread Information

Title
Help tracing ring main in singles
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
8
Unsolved
--

Advert

Thread statistics

Created
Alan Marriott,
Last reply from
timhoward,
Replies
8
Views
5,870

Advert

Back
Top