Hi guys & gals,

Wonder if anyone can help with my problem
Fitted a new honeywell RF2 pack 3 Heating controller with wireless room stat & cylinder stat for my neighbour a few days ago, which replaced a honeywell ST699B programmer.
The boiler is a Ideal Mexico Super 2 RS50 which i believe is wired as a C plan but without a motorised valve, its gravity HW with a pump on the CH which is located in the boiler itself. There was no cylinder stat fitted either.
There is no wiring centre as such, just a couple of connector blocks which were behind the old programmer to joint the original room stat cable. I replaced it for a wireless system due to damage to the stat cables.


The attached photo shows the wiring diagram for the boiler, which has a gas valve operated via a thermostat in the boiler.
It was wired as it shows and I connected the HW line to LB at the boiler and the CH line to LP along with neutral & earth too the supply & the pump.
However upon setting up the system the gas valve failed to operate when either HW 0r CH or both were called for, the pump however was running on both. I then linked out the 2 lines & that operate the gas valve when either HW or CH was called for. However now when the HW is switched on the CH also activates.


It does say in the honeywell manual that for gravity HW systems a suitable valve should be fitted however thats not an option.


Any ideas how i sort this out for them ?
Cheers
Graeme
IMG_0385.jpg
 
Hi guys & gals,

Wonder if anyone can help with my problem
Fitted a new honeywell RF2 pack 3 Heating controller with wireless room stat & cylinder stat for my neighbour a few days ago, which replaced a honeywell ST699B programmer.
The boiler is a Ideal Mexico Super 2 RS50 which i believe is wired as a C plan but without a motorised valve, its gravity HW with a pump on the CH which is located in the boiler itself. There was no cylinder stat fitted either.
There is no wiring centre as such, just a couple of connector blocks which were behind the old programmer to joint the original room stat cable. I replaced it for a wireless system due to damage to the stat cables.


The attached photo shows the wiring diagram for the boiler, which has a gas valve operated via a thermostat in the boiler.
It was wired as it shows and I connected the HW line to LB at the boiler and the CH line to LP along with neutral & earth too the supply & the pump.
However upon setting up the system the gas valve failed to operate when either HW 0r CH or both were called for, the pump however was running on both. I then linked out the 2 lines & that operate the gas valve when either HW or CH was called for. However now when the HW is switched on the CH also activates.


It does say in the honeywell manual that for gravity HW systems a suitable valve should be fitted however thats not an option.


Any ideas how i sort this out for them ?
Cheers
Graeme
View attachment 15102

Page 4 C plan.

http://www.honeywelluk.com/documents/Full-Install/pdf/1107.pdf
 
Connect 6 to 10. It is always recommended you fit a zone valve on the hot water to get proper control over the hot water.


So how does the boiler fire when you call for CH to operate, if the line only goes from term 4 through 9 then to the pump ?
 
This system gravity hot water, pumped central heating was never designed to have the central heating on with out the hot water. Just the way it was designed
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Help Wiring Honeywell Rf2 Pk3 Controls To Existing System Boiler
Prefix
N/A
Forum
Central Heating Systems
Start date
Last reply date
Replies
5

Advert

Thread statistics

Created
gnselectricals,
Last reply from
Megavolt,
Replies
5
Views
2,448

Advert