Evening all,

I carried out an EICR on a property with economy 7.

I tested the main board like normal and only carried out the dead tests on the econemy 7 board. I have read the forum suggests about the live tests and taken notes for later tests with econemy 7. For now I am just going to put it as a Lim.

My question is in the box that asks how many sources do I put 2?
 
Is your customer happy with you missing out essential tests?

You wrote down the number of sources of supply that there are. Assuming that there is only the public supply then the answer is one. If they also have another source such as PV or a backup generator then you record the appropriate number
 
Evening all,

I carried out an EICR on a property with economy 7.

I tested the main board like normal and only carried out the dead tests on the econemy 7 board. I have read the forum suggests about the live tests and taken notes for later tests with econemy 7. For now I am just going to put it as a Lim.

My question is in the box that asks how many sources do I put 2?

A LIM is only really appropriate when the observation or test falls under the remit and description of the agreed limitations listed at the start of the report. This should be agreed with the customer before the inspection begins.
 
Thanks for the quick response. I told the customer that I cant do a live test on the Economy 7 board because there being no power. He said he was happy. He had the test done because his insurance stipulated it.

Now I know that its acceptable to link off the other board then I will do this and go back in case his insurance are not happy with me not doing this essential test :38:. I did consider this at the time but thought that it was defeating the purpose of testing the loop back as I was using the other incoming supply to loop back.

Because also at the time I didn't know that it was same supply. All knew was that economy 7 was cheaper electric that switched on at night.

Thanks again
 
What do you mean by link off of the other board??
You use the alternative test method of putting a L-E link at the far end of the circuit and testing from the Incoming 24hr L and the outgoing side of the off peak board main switch with the ocpd closed for the circuit being tested. Apart from a short bit of tails it's exactly the same loop you are testing.
 
What do you mean by link off of the other board??
You use the alternative test method of putting a L-E link at the far end of the circuit and testing from the Incoming 24hr L and the outgoing side of the off peak board main switch with the ocpd closed for the circuit being tested. Apart from a short bit of tails it's exactly the same loop you are testing.

OK, can you tell me where I stick each lead for the ZS test after I have the L - E at the far end of the circuit I am testing please. I want to tell you what I think you mean but scared of looking like an idiot haha
 
OK, can you tell me where I stick each lead for the ZS test after I have the L - E at the far end of the circuit I am testing please. I want to tell you what I think you mean but scared of looking like an idiot haha

Don't worry about looking like an idiot, you did that in your first post.

I'm not convinced it's a good idea to advise you on carrying out live testing as you appear to be lacking in knowledge and may not realise the dangers which I would consider to be obvious
 
OK, I dont lack the knowledge I just don't comprehend what you are advising as you are suggesting linking the L-E. As for the idiot thing you should would your neck in. :rifle:
 
OK well i search older post and this has come up before and no one has answered it.

I am sure that if someone could answer clearly it would help others after me. I am off to bed now. If no-one comes back with an answer. I will find out and come back with it.
 
What Dave was suggesting (I think), which is the way I have done it, is link the L-E at the far end of the (hopefully dead ;) ) circuit and measure your Zs across the open time clock/contactor terminals, one of which will be a live feed, if you draw the circuit out you would see this works out electrically the same as measuring at the far end on a conventional circuit.

A search on here for "alternative RCD test" might give you some results, this is similar in that you can do a Hi Zs test across the open RCD giving more accurate results than the no trip test, we also did it this way in the past when a Hi test would trip 6A B type MCBs.
 
Not all economy 7 or 10 have a time clock.
They are fed directly from the meter.
Technically they are a separate installation.
There are two methods for testing:
One is to wait until the board is live.
The other is to take a feed from the normal board to the Off peak board.
Another method is not to conduct live tests at all.
 
Last edited by a moderator:
Not all economy 7 or 10 have a time clock.
They are fed directly from the meter.
Technically they are a separate installation.
There are two methods for testing:
One is to wait until the board is live.
The other is to take a feed from the normal board to the Off peak board.
Another method is not to conduct live tests at all.

Thank you.

I phoned the NICEIC. They said that I can do the follwing:

1) wait until it becomes live.
2 ) calculate the zs as per OSG section 10.3.6
3) phone the dno .

I said about linking over. They said they wouldn't recommend doing that for obvious safety reasons
 
Perform R1+R2 tests, calculate Zs's using measured Ze from main DB, note on cert you have done this, job done. Am I missing something here? Only reason to link would be if RCD/RCBOs present on e7 board.
 
OK, I dont lack the knowledge I just don't comprehend what you are advising as you are suggesting linking the L-E. As for the idiot thing you should would your neck in. :rifle:

Yes you do!
Search YouTube for the video by Chris kitcher where he demonstrates the alternative Zs test method. It has also been posted on here before.

You link L-E at the far end of the circuit with the breaker open, then test from the incoming (live) side of the breaker to the outgoing (earthed) side of the breaker. It is exactly the same circuit as you test by having the tester at the far end of the circuit except you connect the tester at a different point. Draw the two methods out if you don't believe me.
To modify it for the off peak board just test from the incoming live of the 24hr board to the dead side of the main switch of the off peak board with the breaker for the circuit closed.

Also use this circuit for testing central dimming system outgoing circuits, link at far end of circuit and test across the dimming circuitry with breaker open.
 
Not all economy 7 or 10 have a time clock.
They are fed directly from the meter.
Technically they are a separate installation.
There are two methods for testing:
One is to wait until the board is live.
The other is to take a feed from the normal board to the Off peak board.
Another method is not to conduct live tests at all.

Third method is the alternative Zs test using the 24hr L
 
Thank you.

I phoned the NICEIC. They said that I can do the follwing:

1) wait until it becomes live.
2 ) calculate the zs as per OSG section 10.3.6
3) phone the dno .

I said about linking over. They said they wouldn't recommend doing that for obvious safety reasons

Calculating the Zs is a waste of time unless you have all of the parallel paths exactly measured to factor into the equation.
 
Perform R1+R2 tests, calculate Zs's using measured Ze from main DB, note on cert you have done this, job done. Am I missing something here? Only reason to link would be if RCD/RCBOs present on e7 board.

Waste of time calculating, you might as well not bother at all.
 
To my mind, when completing the form for test results, only the results from tests performed should be recorded.
In this particular instance, (unless the normal live is linked to the off peak board), I would just perform and record R1+R2, polarity and IR.
 
Last edited by a moderator:

Reply to Help with filling out EICR with economy 7 in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, need some advice, I moved over from Sse in 2020 to Octpus energy. Whilst I was with SSE I was on E10 when I went over to octopus they put me...
Replies
1
Views
447
Hi, So I'm trying to understand what's going on with my off-peak electricity supply, as something's wrong with it and I'm trying to determine if...
Replies
5
Views
1K
Need help with a quote here. I’m wanting some sound advice. Was called out to the hot water not working so repaired the issue within the panel...
Replies
10
Views
1K
Had an enquiry where the installation (commercial) is relatively new and client has requested a condition report. Probably 80-100 circuits plus...
Replies
8
Views
1K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
831

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock