evening all,
went to look at a mates cu the other day tt system 30ma rcd main switch tripping out randomly
earth loop to stake 150 ohms.
earth loop with everything connected 1.30 ohms.
before i did any insulation tests i did a full set of rcd tests and it wouldnt trip via my tester (mft1552) however test button did work,

so said i would change cu as replacement main switch for old cu not available,
replaced cu today with wylex dual rcd cu tested circuits as i put them back.

now the odd thing there is one lighting circuit that tests >299 l-n >299 l-e >100 n-e when i connect this it stops the rcd from tripping on test.
swapped rcds round and tried circuit on both side of cu but with this circuit connected rcd will not trip, with it removed it will.

what sort of issue can stop the rcd from tripping

for those who dont know me i am 22yrs time served with 2391



at the mo the circuit is just via mcb not on either rcd
and i am waiting to here if random tripping has stopped

thanks mark
 
at what point on the install did you test the RCDs...at the RCD itself...or further downstream...at a socket perhaps....its just i1`v heard of RCBos that wont test upclose to em...but a bit further downstream...
 
With the L/E/N on the light circuit removed from board did you do a continuity and ohms measurement test from the disconnected ends of the circuit to L/E/N on the board just to double check there isn't a interconnection ?
J
 
Why dont you connect the light circuit switch all the lights off at the switch then test the rcd if this works then move on to switching each individual light on until you get the same problem.
 
i did try with all lights on and all lights off still the same but will try again one by one as head was
spinning by this point
Me thinks that if you switch each light off on the suspect circuit and the rcd should work then switch one on at a time and if you do track it down to a section that has transformers on it then this needs to be highlighted to the manufacturer and even safety standards as there could be a lot of rcds up the country that will not trip and that aint good.

Plus have you thought about writing to the rcd manufacturer I take it , it was the same make and model you replaced ?
 
Lets deal with this in a logical manner.
So , did you carry out the rcd tests at the CU with all mcbs switched off ?
Did the both rcds test ok with regards to trip times ?
If they did then we know the problem is not the rcds.
 
I wonder if there are lots of transformers in the circuit,I'm thinking that somehow it is replicating no trip test meter operations, by somehow saturating the circuit with Dc
But that was D-loc....the Robin testers used it...no good on modern RCDs Des..as they will detect D-loc.....
 
yes there is some but not a huge number i did try to trip the rcd both loaded and unloaded

could you explain your comment as i dont understand

Most gadgets and appliances create "electronic noise" on a circuit which can affect rcd testing - which is why mcbs should be switched off at the time of testing.
 
look....i think its now clear that something on that lighting circuit is causing the RCDs not to let go....so now its been narrowed down to a final circuit...lets start to look at that.....i mean this is standard fault finding practice surely guys...
 
Most gadgets and appliances create "electronic noise" on a circuit which can affect rcd testing - which is why mcbs should be switched off at the time of testing.

My ELECSA assessor, told me to test at a socket or light even on a DB change where you might not be 100% certain of having everyting unplugged or disconnected.
 
it has to be something that is common to BOTH RCDs from this one lighting circuit for them both not to want to trip....that means the earth bar........
 
My ELECSA assessor, told me to test at a socket or light even on a DB change where you might not be 100% certain of having everyting unplugged or disconnected.

I couldnt give a rats --- what your assessor says lol.
And if all the mcbs are turned off it doesnt matter whats plugged in or not ???

:41:
 
I made the suggestion about equipment perhaps being the problem because,I trust Mark has carried out all the usual tests we would normally do,he has happened upon an unusual problem that requires an unusual cause

I made the reference to the no trip test of a loop tester to give comparison to what I was dreaming about

Dreaming,because I have no technical know how whatsoever, regards the intricacies or the workings of the rcd tester

I did however find this bit of information from a study into the effects

DC in Residual Current Devices
The widespread use of semi-conductor
devices in domestic, commercial and industrial equipment may result in the
flow of non-sinusoidal earth fault currents in the event of equipment insulation
failure. This can occur in certain circumstances where the waveform may be
rectified or chopped and these waveforms are said to contain a pulsating d.c.
component which may desensitise a standard Type AC RCD.

The above is somewhere along the lines of what I was thinking,it may be utter bullcarp and the problem will likely be standard, but its certainly an unusual cause


Some of the equipoment listed includes Phone chargers invertors,transformers etc
 
I made the suggestion about equipment perhaps being the problem because,I trust Mark has carried out all the usual tests we would normally do,he has happened upon an unusual problem that requires an unusual cause

I made the reference to the no trip test of a loop tester to give comparison to what I was dreaming about

Dreaming,because I have no technical know how whatsoever, regards the intricacies or the workings of the rcd tester

I did however find this bit of information from a study into the effects

DC in Residual Current Devices
The widespread use of semi-conductor
devices in domestic, commercial and industrial equipment may result in the
flow of non-sinusoidal earth fault currents in the event of equipment insulation
failure. This can occur in certain circumstances where the waveform may be
rectified or chopped and these waveforms are said to contain a pulsating d.c.
component which may desensitise a standard Type AC RCD.

The above is somewhere along the lines of what I was thinking,it may be utter bullcarp and the problem will likely be standard, but its certainly an unusual cause


Some of the equipoment listed includes Phone chargers invertors,transformers etc
hey no probs Des...i wasn`t having a go mate....it was just a bit of info i picked up some time ago about the old robin D-loc...thats all mate...
 
just to clarify as of now the board has 4 circuits on one rcd and these all test and behave normaly

3 circuits on the other rcd and they also test and behave normally

the problem circuit is just on mcb at mo but would effect either rcd if connected

have just had text to say nothing has tripped since i left at 1pm and on the old board it was going upto 10 times a day

so i am wondering if i have a transformer or something that tested ok cold after cu change but is stopping rcd tripping and also when it gets hot causes insulation fault remember l-e 299 n-e 100
 
I remember going to a job a collegue had been to..... Rcd main switch not tripping so he ordered a new one and i went to fit it on his day off.
When i went to test it, wouldnt trip either so i did my tests and found a low resistance fault between Neutral and earth which turned out to be a trapped neutral in the fused spur. So sorted that and then checked both rcds and both were fine.
Just an idea
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
norfolk

Thread Information

Title
help with rcd problem
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
53
Unsolved
--

Advert

Thread statistics

Created
Mr Mark Sparks,
Last reply from
Mr Mark Sparks,
Replies
53
Views
5,436

Advert

Back
Top