Getting back to the original post (which probably isn't the main point here now) I am surprised by a lot of the responses here.
A 40 amp cooker? That is maximum theoretical demand, I would be surprised if it had a draw of more than half that for any length of time long enough to cause overload. A 32 or even a 25 would be OK, even at Christmas. 32 would allow some capacity for when the sockets are in use at the same time. The regs do not say that you need a 40 amp breaker for a 40 amp domestic cooker.
2.5mm spur off of a 6mm? Who said a 32 is not allowed? You can have a 2.5 spur of of every socket on a ring with a 32. Sounds like it is less than 3m too, so it can be fused at the far end, being the sockets. Whoever said swap them to SFCU's had a good idea. Do them both and hard wire the appliances. What is wrong with that?
To be honest, if it was an EICR you could say that the cable was effectively protected by the load, being 13a or less, fused plugs.
The only issue of note that would bother me is the inaccessible junctions, done by someone who thought it is OK to do this in the first place. If I had reason to belive it was a sub-standard joint, based on other work in the installation, I would disconnect it at the sockets as someone else said, and run a spur on the surface hidden behind the kitchen units if poss.
But then back to the real point, Jay-Snow, you really should have sussed it out first with some simple testing, especially if using it as a Nicey inspection. Know your adversary, whether it is the client, the job or you.
Cr. Ed