Hi

I am trying to create a thermal cutout circuit to protect a large (10sqm) silicone heat pad table. The total heat pad load is around 30A (split between seven 1kW heat pads), running off a single phase 32A supply. The heaters are controlled with Eurotherms and SSRs, which fail in the closed position. Because of this I want to add thermal switches, but in a manually-resetting circuit. Due to the size of the table, the switches will be very hard to reach (wedged underneath a 500kg steel plate), hence why I dont want to just use thermal fuses.

The max table temp is 90deg, so I was planning to use 110deg switches to switch off the power to the control box via a power relay, the power relay is initially switched on by use of a momentary switch. Once the relay is closed, the coil is powered by the mains supply, until a thermal switch breaks this circuit and powers off the relay. The control box will then not power back on until the thermal switches have closed again, and the momentary switch is manually pressed. See diagram below.

1630924914655.png


However, I cannot find a power relay to these specs. The link below is the closest I could find, but contact rating is only 30A.


I am slightly worried that the right components don't exist because my design is wrong in some way. So if anyone can help with the correct components or a new design that would be amazing.

Thanks
 
If the heating elements each have their own thyristor switches then you will have to include an over temperature sensor to monitor each element t- the sensors wired as a daisy-chain. If the elements are all controlled by one thyristor switch then one might consider only monitoring only one element and regard it as a proxy for all the others - but I think/regard this to be poor design and each should be monitored , especially since the sensors - are relatively cheap. I think too you ought to have a digital thermometer actually measuring the temperature at various locations via selectable sensors placed over the heating table.

The advice on doing a risk assessment and failure modes is very good albeit it may seem like putting obstacles in your way - you want a working, reliable and safe product.

PS: I see my esteemed colleagues have said as much already - we are a chorus then :)
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
london
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Manufacturer / Distributor / Supplier / Inventor - etc
If other, please explain
Mechanical Engineer
Business Name
FAC Technology

Thread Information

Title
High power manually-reset thermal cutout solution
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
16
Unsolved
--

Advert

Thread statistics

Created
atjb6014,
Last reply from
James,
Replies
16
Views
4,251

Advert

Back
Top