Discuss High Zs on ring final circuit in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

robo83

-
Reaction score
40
Good morning,

I was recently at a job and had a discussion with another Electrician regards a high Zs reading on a ring final circuit.

R1+R2 measured 1.68ohm
Ze 0.18
Tncs

This puts the circuit over the permitted zs. I begun seeking out the issue.

However the other electrican said although this was above the permitted zs it can be noted on the cert as 'zs doesn't not comply but rcd protection on the circuit so1667ohms permitted'

Can somebody enlighten me please. Ive sent this on TT Installs but wouldn't expect this to be allowed on a tncs?



Sent from my SM-N910F using Tapatalk
 
Sounds like its either a poor design or a fault, and neither should be accepted because rcd protection is in place. RCD's fail from time to time.
What is r1, r2, and rn?
 
Last edited:
Good morning,

I was recently at a job and had a discussion with another Electrician regards a high Zs reading on a ring final circuit.

R1+R2 measured 1.68ohm
Ze 0.18
Tncs

This puts the circuit over the permitted zs. I begun seeking out the issue.

However the other electrican said although this was above the permitted zs it can be noted on the cert as 'zs doesn't not comply but rcd protection on the circuit so1667ohms permitted'

Can somebody enlighten me please. Ive sent this on TT Installs but wouldn't expect this to be allowed on a tncs?



Sent from my SM-N910F using Tapatalk


What was the Measured Zs and what OCPD are you using?
 
Good morning,

I was recently at a job and had a discussion with another Electrician regards a high Zs reading on a ring final circuit.

R1+R2 measured 1.68ohm
Ze 0.18
Tncs

This puts the circuit over the permitted zs. I begun seeking out the issue.

However the other electrican said although this was above the permitted zs it can be noted on the cert as 'zs doesn't not comply but rcd protection on the circuit so1667ohms permitted'

Can somebody enlighten me please. Ive sent this on TT Installs but wouldn't expect this to be allowed on a tncs?



Sent from my SM-N910F using Tapatalk

Without the Zs reading how on earth do you expect us to be able to offer a helpful comment?


Sent from my iPad using Tapatalk
 
Hi,

R1 = 0.29
Rn = 0.30
R2= 1.30

Measured zs 1.48

The socket in question was a spur, the rest of the ring was highest reading 0.42 r1+r2

OCPD 32amp was on the circuit.

Sent from my SM-N910F using Tapatalk
 
So there's surely an issue with your CPC (it should be around 0.5 ohms for 2.5/1.5mm T+E) on that spur. I would suggest it needs resolving before signing off.
 
We checked sockets, re tightened everything.

Changed mcb to a 20amp.

We are back there tomorrow, will re check.



Sent from my SM-N910F using Tapatalk
 
Hi,

R1 = 0.29
Rn = 0.30
R2= 1.30

Measured zs 1.48

The socket in question was a spur, the rest of the ring was highest reading 0.42 r1+r2

OCPD 32amp was on the circuit.

Sent from my SM-N910F using Tapatalk


I am not trying to be difficult but your notes don't make sense. Are you saying the only socket where the Zs is high is at the spur? If so remove the socket and test to the cable.
 
Last edited by a moderator:
Hi,

R1 = 0.29
Rn = 0.30
R2= 1.30

Measured zs 1.48

The socket in question was a spur, the rest of the ring was highest reading 0.42 r1+r2

OCPD 32amp was on the circuit.

Sent from my SM-N910F using Tapatalk


32Amp cb what sort b,c??
 
I am not trying to be difficult but your notes don't make sense. Are you saying the only socket where the Zs is high is at the spur? If so remove the socket and test to the cable.
Hi Murdoch,

That's correct and I will be tomorrow. , I noticed the high Zs prior to board change as I did pre tests and had the discussion with another Sparks who said he notes on his certs rcd protection. I said wasnt correct which brings me here.

I put the the circuit onto a 20amp tybe B until tomorrow as I've got to return with test cert.

Everything else was spot on apart from the other sparks who was there. No test cert, no Sleveing on cpc. No rcd on outdoor lighting, also the swa was just run along garden.

Sent from my SM-N910F using Tapatalk
 
Hi Murdoch,

That's correct and I will be tomorrow. , I noticed the high Zs prior to board change as I did pre tests and had the discussion with another Sparks who said he notes on his certs rcd protection. I said wasnt correct which brings me here.

I put the the circuit onto a 20amp tybe B until tomorrow as I've got to return with test cert.

Everything else was spot on apart from the other sparks who was there. No test cert, no Sleveing on cpc. No rcd on outdoor lighting, also the swa was just run along garden.

Sent from my SM-N910F using Tapatalk

If sockets are rarely used, the contracts are often poor. Plug your tester in and out a few times to see if the reading varies.
 
Thanks Murdoch,

I mention before I have mainly done commercial so old school houses are become the norm.

One thing for sure, if I'm not sure the yellow book appears. I also post here to seek everyone's opinions.

Many thanks

Sent from my SM-N910F using Tapatalk
 
Thanks Murdoch,

I mention before I have mainly done commercial so old school houses are become the norm.

One thing for sure, if I'm not sure the yellow book appears. I also post here to seek everyone's opinions.

Many thanks

Sent from my SM-N910F using Tapatalk


Not sure I understand this reply, is that due to tapatalk?
 
Thanks Murdoch,

I mention before I have mainly done commercial so old school houses are become the norm.

One thing for sure, if I'm not sure the yellow book appears. I also post here to seek everyone's opinions.

Many thanks

Sent from my SM-N910F using Tapatalk

Did you not test properly doing commercial? Testing is testing irrespective of the type of installation
 
Hi,

R1 = 0.29
Rn = 0.30
R2= 1.30

Measured zs 1.48

The socket in question was a spur, the rest of the ring was highest reading 0.42 r1+r2

OCPD 32amp was on the circuit.

Sent from my SM-N910F using Tapatalk

So the socket in question is a spur of the ring main and not part of the actual ring main?
 
Did you not test properly doing commercial? Testing is testing irrespective of the type of installation
Did mainly metal munching on rail projects. Domestic is another ball game and I'm sure you would respect that although testing is testing it's a bit different when u had Bob the builder playing games compared to a fresh install.

Sent from my SM-N910F using Tapatalk
 

Reply to High Zs on ring final circuit in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Hi Guys. When measuring zs I get very high reading. Ze is 0.3 (tns), zdb is 0.21. r1 and rn are is 0.42. r2 is 0.72 , r1+ r2 is 0.29 . when I...
Replies
27
Views
7K
Can you get the zs by using a earth loop impedance tester. I was taught if there's 2 rings circuits, you can do r1,r2, rn /4 on 1 On the other...
Replies
6
Views
5K
I've just finished an installation on a large outhouse around 50 meters from the main property, but I'm having issues with unusually high Zs...
Replies
11
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock