CU in hallway, water pipes into house are out the front door and round the other side of the house. Probably a 6 -7m main bonding conductor.

a) Is this safe?

b) Is there a way of testing it without using really long leads?

Cheers,

Ahab
 
CU in hallway, water pipes into house are out the front door and round the other side of the house. Probably a 6 -7m main bonding conductor.

a) Is this safe?

b) Is there a way of testing it without using really long leads?

Cheers,

Ahab

You answered your own question, you use an R2 long lead test to ascertain the resistance of the bonding conductor.

This should be within approximately 0.05 Ohms

Your 'is it safe' question is quite surprising, what experience do you have?
 
long lead. null leads with long lead in circuit. test bond, job done
 
Yes basically "method 2 - R2" we had to do this in an old peoples home when it was empty, just make sure you null the whole lead.
 
Unless you can physically trace the cable, then you should really isolate the supply to the installation in question and disconnect the cable at both ends and then carry out the continuity test.

This is only my opinion, so please don't take it literally as being correct.
 
lol that why I said it was empty because we had to disconnect the supply which we made sure it was safe to do.
 
Unless you can physically trace the cable, then you should really isolate the supply to the installation in question and disconnect the cable at both ends and then carry out the continuity test.

This is only my opinion, so please don't take it literally as being correct.

Just for 2391-10 students, the installation should always be isolated when testing main protective bonding conductors.
The method in Guidance Note 3 recommends the disconnection of one end of the conductor to avoid parallel paths.
 
Your 'is it safe' question is quite surprising, what experience do you have?[/QUOTE]

Thanks for the answer. I suppose it was a bit of a dumb question with hindsight as a little thought process would tell me that as long as the ohms are low enough it is safe. What I meant was, since I don't know anything other than the 17th ed, is there anything that was allowed in previous editions of the regs that wouldn't be now, e.g. Is running the main bonding conductor along the outside of the house acceptable? I'm just starting out to be honest and want to get things right, but don't know the BRB back to front yet.

Thanks to all for the surprisingly quick answers BTW.
 
Just for 2391-10 students, the installation should always be isolated when testing main protective bonding conductors.
The method in Guidance Note 3 recommends the disconnection of one end of the conductor to avoid parallel paths.

I disconnect it at both ends to identify as well as the continuity test so I can cable tie a tag displaying the words Gas or Water or Steelwork and that's in all honesty and that was a requirement of the nic for a new install so I used to carry it out on remedials while carrying out pirs.
 
Your 'is it safe' question is quite surprising, what experience do you have?

Thanks for the answer. I suppose it was a bit of a dumb question with hindsight as a little thought process would tell me that as long as the ohms are low enough it is safe. What I meant was, since I don't know anything other than the 17th ed, is there anything that was allowed in previous editions of the regs that wouldn't be now, e.g. Is running the main bonding conductor along the outside of the house acceptable? I'm just starting out to be honest and want to get things right, but don't know the BRB back to front yet.

Thanks to all for the surprisingly quick answers BTW.[/QUOTE]

It's unusual, the bond is normally carried out at the point of entry to the building.
 
as long as the cable is not prone to be damaged, no problem. any chance of mechanical damage, it should be protected in conduit. are there hungry squirrels about the property?
 
The outside cable can be made squirrel proof by

A, Enclosing the cable in conduit or
B, Make sure the squirrel has an abundance of nuts or
C, Buy a cat
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
How do you test main bonding when it's several meters long?
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
14

Advert

Thread statistics

Created
Capn Ahab,
Last reply from
Des 56,
Replies
14
Views
10,326

Advert

Back
Top