dis agree with this part of your reply there is a reason why the fans have to be de rated and the reason is if the fan seizes to to lack of maintainance or a failure of the bearings etc which causes the fan to stop then the fan motor could over heat and catch fire this could be before a 6 amp or 10 amp mcb operates hence the reason it has been de rated i have been in a situation where this has happend and has set fire to a shop causing £89,000 worth of damage , also a fan in a toilet of a hair dressing salon luckly didnt cause much damage , and one main one was due to a fatal fire in which 3 people died in London which the spark was prossecuted , not sure what the outcome was this is the reason for derating

That may be true. Is there evidence that a 3A fuse would have prevented the outcome?

The CU fusues/mcbs are there to protect the installation cables. These fans are not supplied with fitted 3A flex.

If the manufacturers produce products which are 1A (or even ¼A) then they should fit integral fuses rather than state that another accessory be fitted to the installation which is still three times (or even twelve times) larger than necessary.

I suggest that this tragedy would be due to the manufacturers' negligence were it not for 134.1.1 allowing them a cop-out and/or to produce shoddy goods.

That's what I meant by unnecessary.
 