Hi guys, I need to have an induction hob and oven connected up. Units are:
Hob: AEG HK654400XB Induction hob - HK654400XB | AEG - https://www.aeg.co.uk/kitchen/cooking/hobs/induction-hob/hk654400xb2/
Oven: Miele H2561BP Miele Ovens | H 2561 BP Oven - https://www.miele.co.uk/domestic/ovens-1451.htm?mat=10116060&name=H_2561_BP
There is an existing cooker circuit with isolator. Each wire, pos and neg, inside the isolator has an outer diameter including PVC cover of 5mm. So I need to know:
1. What the existing wiring is in cable size/capacity
2. If this is enough allowing for diversity
3. Or do I need a new feed from the fuse box for the induction hob, which seems the more greedy of the two.
Can someone fill me in on where to go here? I do know some basic DIY electronics so would understand ratings.
generally, the existing circuit would be 6mm ( cross section, not diameter)and that is fine for up to 15kW (total rating) of cooking appliances. what size MCB is protecting the cable? best advice is to get a local spark to check and test the circuit and then advise on whether it will cope .
The cooker fuse for the existing circuit is 45A. Not sure if the cable is 6mm or 10mm. Can anyone give me a definitive answer based on the fact that the OD of each single wire is 5mm including PVC cover? What's that?
You could always measure the diameter if you're really that unsure.
10mm² ((√(10/π)) x 2) = 3.56mm diameter.
6mm² ((√(6/π))x 2) = 2.76mm diameter.
4mm² ((√(4/π))x 2) = 2.25mm diameter.
More tricky than that. The cable will be composed of 7 strands, so measure a strand, apply the formula and multiply by 7 to get the measured csa of the cable.
Hope you have a micrometer!
Not so easy, this electrickery stuff, is it?
Sounds like 6mm. Looking up Farnell specs, 6mm total OD is 4.85mm, rated 48A. Fuse is 45A That sounds close. 10mm is OD 6.3mm which is more than the 5mm I measured.
Using Ohm's law, 230v at 48A is 11kW which is what's required in total. Looks borderline but not impossible.
Earth is insulated yellow/green. Wiring was put in in the 1980s.
he's basically saying that you are out of your depth and should seek the services of an electrician.
London
Induction hob plus oven wiring - rating?
les24preludes,
les24preludes,