Hi guys, I need to have an induction hob and oven connected up. Units are:
Hob: AEG HK654400XB Induction hob - HK654400XB | AEG - https://www.aeg.co.uk/kitchen/cooking/hobs/induction-hob/hk654400xb2/
Oven: Miele H2561BP Miele Ovens | H 2561 BP Oven - https://www.miele.co.uk/domestic/ovens-1451.htm?mat=10116060&name=H_2561_BP

There is an existing cooker circuit with isolator. Each wire, pos and neg, inside the isolator has an outer diameter including PVC cover of 5mm. So I need to know:
1. What the existing wiring is in cable size/capacity
2. If this is enough allowing for diversity
3. Or do I need a new feed from the fuse box for the induction hob, which seems the more greedy of the two.
Can someone fill me in on where to go here? I do know some basic DIY electronics so would understand ratings.
 
generally, the existing circuit would be 6mm ( cross section, not diameter)and that is fine for up to 15kW (total rating) of cooking appliances. what size MCB is protecting the cable? best advice is to get a local spark to check and test the circuit and then advise on whether it will cope .
 
The cooker fuse for the existing circuit is 45A. Not sure if the cable is 6mm or 10mm. Can anyone give me a definitive answer based on the fact that the OD of each single wire is 5mm including PVC cover? What's that?
 
More tricky than that. The cable will be composed of 7 strands, so measure a strand, apply the formula and multiply by 7 to get the measured csa of the cable.
Hope you have a micrometer!
Not so easy, this electrickery stuff, is it?
 
Sounds like 6mm. Looking up Farnell specs, 6mm total OD is 4.85mm, rated 48A. Fuse is 45A That sounds close. 10mm is OD 6.3mm which is more than the 5mm I measured.

Using Ohm's law, 230v at 48A is 11kW which is what's required in total. Looks borderline but not impossible.

Earth is insulated yellow/green. Wiring was put in in the 1980s.
 
is it a 45A fuse or a MCB? or are you going by the isolator rating?
 
he's basically saying that you are out of your depth and should seek the services of an electrician.
 
OK - 2 points here. I've been designing and building tube amplifiers for 10 years and I can assure you they are complex designs and they all work. I said I was familiar with DIY electronics, tubes in my case. Not electrical house and appliance wiring and the associated regs. That's something else. So please no more sarky comments. I will be using an electrician to do the work - I'm not doing this myself. I'm just planning it at this stage because I want to know if the existing circuit is adequate for the load. Any questions?
 
If it is a flat T&E then having a stranded earth there is every chance it is 10.0, can you show a pic.
 
So please no more sarky comments. I will be using an electrician to do the work - I'm not doing this myself. I'm just planning it at this stage because I want to know if the existing circuit is adequate for the load. Any questions?

Well, we've never heard that before haha.
 
Are you reading this thread? It's stranded with a yellow/green PVC cover.
6.0mm is generally a solid cpc (earth core). 10.0mm is stranded. however, it could be imperial cable, 7/036 or 7/044. sorry to add to the confusion. :(
 
What's your point here - are you referring to me or what?
Yes, I was referring to you. There is no positive and negative in AC circuitry. Well there is, if you look at an AC sine wave.

But my point is that if you are thinking black is -ve and red is +ve, then you need to concentrate on other aspects of DIY than Electricity.

Sorry to be hard, but trying to stop you getting out of your depth.
 
Ah, right. Thanks for that. I have people coming over so no time now. I'm just going on what I can see with a torch inside the insulator, which I can only get about an inch off the wall. It doesn't look like a flat T&E. There are 3 wires, all stranded PVC sheathed. OD of each is 5mm including the sheath. Looking at Farnell specs, 6mm is 4.85mm OD which looks right and 10mm is 6.3mm OD which looks too thick. But as you say, it's not T&E inside the insulator.
 
Ah, right. Thanks for that. I have people coming over so no time now. I'm just going on what I can see with a torch inside the insulator, which I can only get about an inch off the wall. It doesn't look like a flat T&E. There are 3 wires, all stranded PVC sheathed. OD of each is 5mm including the sheath. Looking at Farnell specs, 6mm is 4.85mm OD which looks right and 10mm is 6.3mm OD which looks too thick. But as you say, it's not T&E inside the insulator.
look on the bright side. at least you'll not be tempted into buying a gas oven and sticking your yed in it. :(
 
OK - I see the point about AC. Just not thinking since I build DC circuits in electronics and when I see red and black wires my head goes "pos and neg". So going back to the point of the thread
1. How do I know if this is 6mm or 10mm wiring? 10mm is fine.
2. If it's 6mm wiring, and given the travel is 7 metres from the fuse box, is this circuit Ok for 11kW? Looking into this, I came across the following calculations:
100% of first 10amps and 30% of remaining load, add 5 amps if a 13a outlet in control unit. So 11kw= 47.83amps at 230v
30% of 37.83 = 11.349
11.349+10= 21.349a
So a 6mm cable should satisfy the regs. Does this sound correct?
 
OK - I see the point about AC. Just not thinking since I build DC circuits in electronics and when I see red and black wires my head goes "pos and neg". So going back to the point of the thread
1. How do I know if this is 6mm or 10mm wiring? 10mm is fine.
2. If it's 6mm wiring, and given the travel is 7 metres from the fuse box, is this circuit Ok for 11kW? Looking into this, I came across the following calculations:
100% of first 10amps and 30% of remaining load, add 5 amps if a 13a outlet in control unit. So 11kw= 47.83amps at 230v
30% of 37.83 = 11.349
11.349+10= 21.349a
So a 6mm cable should satisfy the regs. Does this sound correct?
correct. as long as the cable is not covered in insulation, 6.omm .is good for a cooker/oven circuit up to 15kW (allowing for the diversity that you mentioned). you seem to be over complicating the issue.
 
Diversity covers a multitude of sins. I was thinking of a perfect storm like a Christmas dinner with a roasting turkey and four rings on the go on an induction hob. But as you say, that's probably overthinking things. Or alternatively setting the Miele oven on self-clean at the same time as cooking up a few kilos of boiled vegetables for a vegan lunch.... That's probably seriously overthinking it.....
 

Reply to Induction hob plus oven wiring - rating? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, we are replacing our old hob and cooker and I need a bit of help, to make sure all is safe. This is the oven and hob specs: AEG IKB64401FB...
Replies
0
Views
2K
Hi all We are hoping to upgrade our oven. We currently have a single integrated oven and a separate induction hob. Each has its own red switch...
Replies
0
Views
887
Hello I have two new appliances Electric oven rated at 3.95 KW Induction hob rated at 7.2 KW total of 11.15 KW Currently it is on its own...
Replies
17
Views
4K
Hi all, looking for some clarification on MCB and cable sizes I need to run for a new kitchen. Cables will run through a combination of...
Replies
0
Views
3K
Hi, replacing gas hob with Zannusi 7.3kw (max)32a induction hob, and oven with aeg 3.2kw(max) 16a. I was going to put hob on existing 32a 6mm...
Replies
11
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top