Currently reading:
Induction hob plus oven wiring - rating?
Discuss Induction hob plus oven wiring - rating? in the UK Electrical Forum area at ElectriciansForums.net
Hi guys, I need to have an induction hob and oven connected up. Units are:
Hob: AEG HK654400XB Induction hob - HK654400XB | AEG - https://www.aeg.co.uk/kitchen/cooking/hobs/induction-hob/hk654400xb2/
Oven: Miele H2561BP Miele Ovens | H 2561 BP Oven - https://www.miele.co.uk/domestic/ovens-1451.htm?mat=10116060&name=H_2561_BP
There is an existing cooker circuit with isolator. Each wire, pos and neg, inside the isolator has an outer diameter including PVC cover of 5mm. So I need to know:
1. What the existing wiring is in cable size/capacity
2. If this is enough allowing for diversity
3. Or do I need a new feed from the fuse box for the induction hob, which seems the more greedy of the two.
Can someone fill me in on where to go here? I do know some basic DIY electronics so would understand ratings.
generally, the existing circuit would be 6mm ( cross section, not diameter)and that is fine for up to 15kW (total rating) of cooking appliances. what size MCB is protecting the cable? best advice is to get a local spark to check and test the circuit and then advise on whether it will cope .
More tricky than that. The cable will be composed of 7 strands, so measure a strand, apply the formula and multiply by 7 to get the measured csa of the cable.
Hope you have a micrometer!
Not so easy, this electrickery stuff, is it?
Sounds like 6mm. Looking up Farnell specs, 6mm total OD is 4.85mm, rated 48A. Fuse is 45A That sounds close. 10mm is OD 6.3mm which is more than the 5mm I measured.
Using Ohm's law, 230v at 48A is 11kW which is what's required in total. Looks borderline but not impossible.
Earth is insulated yellow/green. Wiring was put in in the 1980s.
he's basically saying that you are out of your depth and should seek the services of an electrician.
OK - 2 points here. I've been designing and building tube amplifiers for 10 years and I can assure you they are complex designs and they all work. I said I was familiar with DIY electronics, tubes in my case. Not electrical house and appliance wiring and the associated regs. That's something else. So please no more sarky comments. I will be using an electrician to do the work - I'm not doing this myself. I'm just planning it at this stage because I want to know if the existing circuit is adequate for the load. Any questions?
Reply to Induction hob plus oven wiring - rating? in the UK Electrical Forum area at ElectriciansForums.net
