in the sequence of tests before the supply ois connected it doesnt state rcd testing comes first
i continutiy oc protective conductors
2continuity of ring
3ir
4pol
5 earth electrode
 
I'm surprised your RCD even stays on with line and neutral to earth readings as low as that!!.
 
in the sequence of tests before the supply ois connected it doesnt state rcd testing comes first
i continutiy oc protective conductors
2continuity of ring
3ir
4pol
5 earth electrode

who said it came first andy? the fact you gave a 0.2 reading was why we asked what the real readings were, now we know what 0.2 has to do with a TT system, but 1 do you? and 2 what has your IR readings mean to you?
 
one of the posters in this topic stated i shouldnt be doing anything if i havent done rcd tests
 
If your insulation tests are poor it is little wonder you aint done any RCD testing. Anyway you originally said you had done RCD testing and you got 0.2 whatever you claim that is supposed to signify!
 
one of the posters in this topic stated i shouldnt be doing anything if i havent done rcd tests

No we asked you to confirm your RCD readings before we would give you any help andy as the reading you gave was at best confusing and you got the 0.2 mixed up from something else to do with them??
 
this is on a lighting circuit with a low voltage transformer connected if that makes any diffrence
 
think OP has had too much beer with female hormones in it. after a skinful, you undergo a sex change.

1. you argue about nothing. 2. you talk a load of irrational crap. 3. you can't drive. 4. you cry for no reason. 5. you can't see past the end of your nose.
 
sounds like your trying to come out without actually admitting it, oh and you forgot the bit about being unable to reverse
 
Forget about the RCD anyway. First up you need to determine if you have installed a low voltage light 230v or an Extra low voltage light 12v. Do you really have an earth connection or not.
Secondly with insulation resistance results like you claim to have i would definately be looking further into the circuit with regards to its condition and suitability to be adding a light and fan onto it in the first place.
 
think OP has had too much beer with female hormones in it. after a skinful, you undergo a sex change.

1. you argue about nothing. 2. you talk a load of irrational crap. 3. you can't drive. 4. you cry for no reason. 5. you can't see past the end of your nose.
Spot on mate!! :D
 
it has a 12v transformer which does not have a seperate earth to connect to the lighting circuit
 
you only IR test to the primary side of the transformer, or, as transformers for this situation are generally class2, to wherever the cpc of the circuit is terminated. ( for details of termination, ask arnold )
 
i have done ir tests at the consumer unut with power off, all lamps removed and all switches on/closed. i did not remove the earth or neutral for the connection bars in the consumer unit when i done tests.
 
So it isn't a low voltage light then. Seriously mate you really need to stop NOW before you end up hurting either yourself or somebody else!
Get somebody qualified to get this sorted. You are working within a special location which requires correct protective measures. You have nothing correct not even a healthy circuit to connect to so stop the nonsense and do the decent thing.....CALL A QUALIFIED ELECTRICIAN!!
 
i have done ir tests at the consumer unut with power off, all lamps removed and all switches on/closed. i did not remove the earth or neutral for the connection bars in the consumer unit when i done tests.
Are the values in the OP ohms on continuity?

Not IR at all.

Don't know why I'm bothering.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Insulation Resistance
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
155

Advert

Thread statistics

Created
andytucker,
Last reply from
Marvo,
Replies
155
Views
10,493

Advert

Back
Top