Hi all,

Well, this one is interesting and I have absolutely no idea what could be causing this.

Just added a PIR to a lighting circuit, very simple, disconnect the lamp and move the feed cables to feed a PIR and then onto the lamp itself. Nice straightforward.

Doing my testing for the minor works cert and the IR readings go something like this:-

2, 10, 100, 200, 450, 4.5, 350, 5.5, 400, 5, and so on.

The ramp up at the beginning I expect to see, but then flipping back and forth between lower values and higher values. All above the minimum 2Mohm, but a cyclic flip back and forth with steady timing.

I didn't test L-N, but the same thing happens on L+N-E, L-E and N-E and it happens at 250v and 500v.

Anyone got any suggestions as to what could cause this because as I say, I've got nothing?
 
i wouldn't worry about it.could be a parallel path. i had a call-out this morning. MCB tripped on a lighting circuit. (fluorescents). IR L-E was 0.00Meg. on continuity was 34 ohms L-E. even after fault was cleared (a cooked ballast), same readings. testing properly was impossible due to being unable to ID which N and E's belonged to the circuit in an originally wired in singles installation with loads of additions bodged on with T/E.
 
It was mixed lighting, the PIR was in circuit because I needed it to be to test as much of the cabling as possible.

If it had been flipping between high and very low (less than 2Mohm) I might have been really worried, but all readings were well above that.

Oh well, one of those things I guess, just never seen anything like it before so figured I'd seek some sage advice :)
 
Why was the PIR in circuit... no reason really, other than just wanting to be thorough and include as much of the final circuit as possible. There's got to be a notification as it's a modified outside circuit, so just wanted to be doubly sure there were no issues.

Change of accessory... one was a change, and that was fine, the other was on the circuit that gave the flip flop readings and that was a change to the circuit.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

SparkyChick

Broke Internet
Esteemed
Supporter
Joined
Location
South Wales
Website
http://www.sparkychick.uk
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
Business Name
SparkyChick

Thread Information

Title
Interesting IR Readings - Any ideas?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
24
Unsolved
--

Advert

Thread statistics

Created
SparkyChick,
Last reply from
SparkyChick,
Replies
24
Views
2,089

Advert

Back
Top