nick611

what is the point of an IR test? yes i know its to show low risistance on cable insullation [its in the name] and that can lead to short circuit and fire risk, but with the protection we use now wont this show its self eventually. what do you tell a customer in a nursing home ? that his IR is a bit low and some time in the future he may get a problem. HE says when,and you say,i dont know,he says,what,and you say,i dont know. AM i the only one who thinks while IR testing with all the ******* hassle that goes with it. WHATS THE POINT
 
Is this a wind up?

no its not, i am asking for your views,this is a forum. how many problems have you identified in advance through IR testing? and how did you overcome them.would you for instance replace a submain because of a low IR before it had caused any real problem.and how would you justify this to the person you wanted to pay for it?
 
i sometimes find low ir on lighting circuits n to e that some sparks had just put on a 60898, we.re putting 61009s on and without the ir test i would have no way of knowing if the rcbo would hold.
 
Sorry Nick but i'm suprised.

Ok IR a circuit on a CU change as many faults that hold in on a fuse/mcb will trip on RCD/RCBO

On a PIR it will give you an indication on an older installation that there can be a problems developing. So you will alter the time frame of the next PIR to say 5 tears or even less.

On an initial verication it will tell you if your circuit as been damaged. You may have first fixed the before someone put a nail through your cable, it will stop you energising the circuit.

Again On fault finding it will help.
 
yes i see but on a domestic 17 edition board the rcd will find any l-e and n-e faults and the mcb any l-n faults so on a piriodic why IR test given the time and hassle [disconecting this and that] it takes. just a thought
 
You are trying to identify any future problems with the wireing in the instalation and if the insulation is starting to deteriorate the customer needs to know. Like Malcolm has said the inspection time can be reduced to see if the problem is getting worse.

Low IR readings don't just indicate that the cable insulation is failing as it could be other issues like dampness getting into joint boxes under the floor etc.

If the IR reading on the whole instalation was low then I would be testing each cct to find out if one particular cct was bringing the readings down and try and locate the cause.

I am sure if you did locate a joint box full of condensation because it was lying on the ground and the readings were now more healthy the customer would be alot happier.

In a Nurseing home I am sure that the insurance company will have there say re the report and they won't be happy to rely on 17th edition boards they will be looking at your report making sure that the home is safe and what needs to be done to keep it that way IMO.
 

Reply to IR test whats the point? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I have been asked to look at this report as the customer has been given (in their words) 'A very high quote plus VAT'. It doesn't look well...
Replies
5
Views
644
Just thinking about selling MFT's and single test equipment. The idea being I buy stuff from Ebay and sell it on ebay, which I am doing at the...
Replies
0
Views
315
Hi, I'm a little confused confused is someone can shine some light on the amendment 2 way of doing IR. I know you have to do one 1st fix at 500V...
Replies
6
Views
2K
Hi Im an apprentice and just wanted to clarify domestic style wiring since i work industrial and don't deal with conventional wiring. in college...
Replies
1
Views
921
Recently changed a CU for a friend and today when visiting one of the RFC's RCBOs tripped. It was due attention anyway as open ring and no time to...
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock