Hi guys could you help me please i have been given this question but i don't think it is right:

An A2 radial circuit is wired in 4mm 2 thermoplastic twin and earth cable. It is 23 meteres long. The circuit has on it 4 twin 13 amp sockets, Protection is by a 30 amp BS 3036 semi enclosed fuse, Ze for the instalation is 0.6 ohms.
socket 1 is 12 metres from the consumer unit, socket 2 is 6 metres from socket 1 and socket3 is is 2.5 metres from socket 2

Calculate the r1 & r2 value at each socket outlet
Will the protective device be suitable

could you let me know what you think the answer is so that i can compare mine

Thanks in advance
acestu
 
Given Ze= 0.6 ohms
A few assumptions here
No rating factors
4mm fte with 2.5cpc
20 c temp
R1+R2 table 9A OSG=12.02mohm/m
Thermoplastic max temp70 c table 52.1
Table41.2 max EFL zs 1.09 for BS 3036 semi enclosed
R1+R2
Sct 1 12m x12.02/1000=0.144ohm
Sct2 18m x12.02/1000=0.216ohm
Sct3 20.5m x12.02/1000=0.246ohm
Sct4 23m x12.02/1000=o.276ohm
Max R1+R2=0.276x1.20(correction factor OSG table 9c)=.3312
Zs=0.6+.3312=0.9312
Calculated Zs =0.9312
Max Zs allowable =1.09
 
Yeah, but given it sounds like an exam question I guess you could in theory have 1.5, 2.5 or 4 for the cpc;-)
 
Ok fellas this is what the answer says:

From table 9a in the on-site guide r1 & r2 value for the 4mm 2 / 1.5mm 2 conductors is 16.71 m ohm /M. The r1 & r2 value at the sockets is

socket 1 = 12 x 16.71 divided by 1000 = 0.2 ohms

socket 2 = 18 x 16.71 divided by 1000 = 0.3 ohms

socket 3 = 20.5 x 16.75 divided by 1000 = 0.34 ohms

Zs will be 0.34 + 0.6 = 0.94 ohms. The maximum zs for 30 amp BS 3036 fuse from table 41B1 in BS7671 (0.4s) is given as 1.14 ohms.

Using the rule of thumb for temperature correction the maximum permitted value is 1.14 x 0.75 = 0.86 ohms. This value is acceptable.


Ok so what does everybody think of th?

Please post your comments

Thanks
Acestu
 
I am only a newbie student but my thoughts first of all were the same as Mr cctbreaker ie what is the csa of the protective conductor, and then when i looked at the answer i thought what has happened to the 4th 13 amp socket surely i use the resistance reading at the end of the radial circuit in order to determine Zs, I thought i was going mad, it seems that this publication is full of mistakes because the first couple of questions seem to have errors

So just be careful if you download this E book

ie A Practical Guide To Inspection & Testing

Cheers
Acestu:confused:
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Is this Question Right ?
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
7

Advert

Thread statistics

Created
acestu,
Last reply from
acestu,
Replies
7
Views
1,855

Advert

Back
Top