  1. shower had incorrect isolation switch
  2. shower wired in 2.5mm cable
  3. shower suppl not on its own circuit
  4. earth not connected for circuit 3
  5. no earth sleeving circuit 4
  6. faulty switch on kitchen socket
  7. every circuit apart from the cooker had failed the insulation resistance test
thus the test conclusion was unsatisfactory.


guy then asked so all i need is to retest in 10 year :S

he was positive he doesnt need to rectify

property was rented out and he was landlord
 
Without meaning to sound like I'm taking a pop at you, which I'm not as I don't know you, are you confident that you are testing correctly? As with those figures something is seriously amiss somewhere.

exactly , its highly unlikely that those IR reading are caused by the cables themselves
more like duff jb's and poor terminations.
i'd be doing more investigating before advising a rewire of pvc thats only 30 years old.
 
i unplugged everything , the shower circuit was in with ring main on 2.5mm ,which had melted in the shower so 0.00 was expected there
surge protected ext i unplugged , didnt test between lives only L-E N-E

really cant understand this
 
I would do a global L-E test first,all breakers on,then 1 by 1 flick off and see where the culprit lies.As mentioned if all circuits were in service its impossible to have 0.00 on L-E without something going BANG.
 
Normally if i get such bad readings on a 25/30 yr old dwelling as you have gave example of. I will get my other meter out to double check. But i have that luxury at the moment. If i didnt i would get my mates to check against.
 
  1. shower had incorrect isolation switch
  2. shower wired in 2.5mm cable
  3. shower suppl not on its own circuit
  4. earth not connected for circuit 3
  5. no earth sleeving circuit 4
  6. faulty switch on kitchen socket
  7. every circuit apart from the cooker had failed the insulation resistance test
thus the test conclusion was unsatisfactory.


guy then asked so all i need is to retest in 10 year :S

he was positive he doesnt need to rectify

property was rented out and he was landlord

What protective device was protecting the shower?
 
are you sure it's not a power shower? and those IR readings would lead me to believe that it's a single neutral fault affecting more than 1 circuit. did you dis. the neutrals from the N bar in the CU before testing?
 

Reply to just failed eicr in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top