I attend a job today and can see the Main earth is via a tag to the SWA lead.

I called DNO and they informed me if the ze is within permitted Tn-s values (which it was 0.20 Ohm) then leave it in place. I requested a PME upgrade and they wasn't keen since this was in place.

Looking for some advice with this, is it permitted or do I convert to TT.

20180831_091121.jpg
 
I suspect if you were to show them a photo of that earth clamp on their lead sheath they may not be so quick to accept it is their earth facility
There again if they have said its Tns why argue the point
 
Looks like a typical tns install, the ze is well within highest limit so there is no need to change it at all. Maybe just upgrade the earth bar there to an enclosed esco
 
I attend a job today and can see the Main earth is via a tag to the SWA lead.

I called DNO and they informed me if the ze is within permitted Tn-s values (which it was 0.20 Ohm) then leave it in place. I requested a PME upgrade and they wasn't keen since this was in place.

Looking for some advice with this, is it permitted or do I convert to TT.

View attachment 44026
SWA Lead??
 
it's not SWA, it's PILS (orPILC for some). that'sacommon way of providing a TN-S earthing. the lead sheathed cable is buried direct and the lead sheath provides the earth. pity about the DIY BS951 clamp though.
 
Problem is if you convert to TT the lead sheath is an exposed conductive part so you would have to leave the earthing conductor in place so this negates the TT.
 
Yeah I wouldn't trust that type of clampon a lead sheath but I also wouldn't touch it either if the Ze is good. What size wire is it between the earth bar and the clamp?
 
Yeah I wouldn't trust that type of clampon a lead sheath but I also wouldn't touch it either if the Ze is good. What size wire is it between the earth bar and the clamp?
Bit of 7/036 by the looks of it, or 4 mm2 for the kids.
 
You could be right with your imperial size, it looks like solid green colour insulation so probably quite old. I was quietly wondering if it was sufficient CSA for the supply...?
 
Thanks for everyone's input.

Pete 999, duly noted. I am reading up on the history of PILS cable now, to further enhance my knowledge.

I am going to call the DNO back when at the job and see if I get another decision/PME upgrade. If Its the same I will note on cert explaining.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Birmingham

Thread Information

Title
Lead sheath SWA as earth
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
13

Thread Tags

Advert

Thread statistics

Created
robo83,
Last reply from
robo83,
Replies
13
Views
4,664

Advert

Back
Top