I got a rcd 30ma 80amp to install, I have no cables to install it, were will I get them says 35mm flexible on the instructions and 50mm rigid.Perhaps you could give us a little more information, maybe also a pic?
Those sound like the maximum the terminals will take.I got a rcd 30ma 80amp to install, I have no cables to install it, were will I get them says 35mm flexible on the instructions and 50mm rigid.
ye that sound good 16mm thanks very much mate, think they call it a split load kit as well.Those sound like the maximum the terminals will take.
Usually the RCD will feed a bus-bar, do you have arrangements for that?
The supply cables (and neutral out to the separate terminals block) have to be sized according to the max current it can expect to carry, that might be limited by the sum of MCBs, or it might be limited by the DNO fuse.
Realistically for 80A you need to look at 16mm as the starting point.
are you familiar with the correct methods of determining minimum size?ye that sound good 16mm thanks very much mate, think they call it a split load kit as well.
Not screwfix or toolstationSplit load kits available in most wholesalers and also screwfix