Thanks for the reply,
Right I've banged my head against wall. I think you could be right. A break would get a reading because...the conductor is broke in half!!!. Because I'am getting a reading could suggest exposed conductor is in direct contact with something giving me the high reading.
I'm i right or still stupid?
Sorry i meant to say you WOULDN'T get a reading from a break in the conductor hence infinity reading
Right...you're measuring the resistance of a single conductor from one end to the other.
In this case...
If you used an IR meter, it would almost certainly read zero.
If you used a LoOhm meter, it would probably read out of range and be mistaken as open circuit.
If you used a regular DMM, it would 2000ohm.
All depends on the range of the instrument you're using.
The question doesn't specify which test instrument was used (it's irrelevant), just the value measured.
Thanks mate,
right ok that makes sense. so ill just go with the 2000 ohms value and treat it as a high res like the first reply said. So this Isn't an open circuit but a loose connection poor join etc?.
Sorry for being a bit slow :)
As I said earlier.. Treat the neutral as a SINGLE lenght of wire with some joints in it. FORGET IR here .... Its NOT complex at all.
Foxhound,
Golden_Boy,