P

piz

Hello
When we are asked to change a CU i have been told on pme and tns the main earthing conductor is the responsibilty of the electricity board.
so if this is the case why is a 16 mm earth sold on packs of 2meter tails?,
example change board 25mm tails or 16mm if 80amp main fuse 10mm to gas and water but only sometimes 4 or 6 mm main earth do we just record this on an EIC
Cheers
 
No you should be changing this to 16mm earth. When they say the earth is there responsibility they mean the earth coming in not the earth wire going to the board.
 
When I do a CU change I always install 16mm or 25mm tails and 16mm earth (25mm for TT).

It is so surprising how many TN-S and TT still have 2mm earths attached.
 
I'm wondering when the thread title will be relevant to the thread

As said in post 2 - the DNO must supply a suitable earth - if they cant provide one within regs then you must supply a TT rod!
The DNO must only make an earth available (if they can) and it is your job then to ensure the cable between the termination of the DNO and the CU is upto regs
 
Pretty pointless exercise then, to have an earth rod that's not buried!! lol!!!

I know your taking the **** - its driven into the ground but the top is exposed - therefore not buried and not protected against mechanical protection - regs states 25mm - I cant be bothered to get OSG or BGB out for the Reg number
 
I know your taking the **** - its driven into the ground but the top is exposed - therefore not buried and not protected against mechanical protection - regs states 25mm - I cant be bothered to get OSG or BGB out for the Reg number
Nicholas I think you have mis-read the OSG.

it says min 25mm if buried but not protected against corrosion

2.5mm if not buried but protected against corrosion and mechanical damage,
4mm if not protected and not buried

 
542.3.1:
Protected against corrosion and mechanical = 2.5mm copper
Protected against corrosion and not mechanical = 16mm copper
Not Protected against corrosion and not mechanical = 25mm copper

Most properties in Pembrokeshire with TT are not protected against corrosion or mechanical protection so must be 25mm

To terminate 25mm into a CU is a pain I had to split the cable to 4/3 wires and terminate that way over 2 connections - NAPIT said that was the best way
 
542.3.1:
Protected against corrosion and mechanical = 2.5mm copper
Protected against corrosion and not mechanical = 16mm copper
Not Protected against corrosion and not mechanical = 25mm copper

Most properties in Pembrokeshire with TT are not protected against corrosion or mechanical protection so must be 25mm

To terminate 25mm into a CU is a pain I had to split the cable to 4/3 wires and terminate that way over 2 connections - NAPIT said that was the best way

That reg refers to the cable being buried directly in the ground, see the extract from the OSG I posted earler
 
Either way in Pembrokeshire its not possible because all the rods have been concreted to make a path - i will take the trunking idea into consideration next time
 
542.3.1:
Protected against corrosion and mechanical = 2.5mm copper
Protected against corrosion and not mechanical = 16mm copper
Not Protected against corrosion and not mechanical = 25mm copper

Most properties in Pembrokeshire with TT are not protected against corrosion or mechanical protection so must be 25mm

To terminate 25mm into a CU is a pain I had to split the cable to 4/3 wires and terminate that way over 2 connections - NAPIT said that was the best way


The PVC sheath is the protection against corrosion. Bare copper conductor is the type of cable not protected against corrosion... I wouldn't use 16mm for a domestic UK TT system with an Ra value hovering around 200 Ohms!! lol!!
 
Either way in Pembrokeshire its not possible because all the rods have been concreted to make a path - i will take the trunking idea into consideration next time

Shame they didn't install a concrete earth rod pit on the rod and buried the earth conductor in the path too!! Why not run this cable in a metal of heavy duty PVC conduit between rod and where it enters the house, even better chasing the cable into the path. Surely got to be better than a a cable running across a pathway??
 
Nicholas I have used a Max csa of 16mm before where there is no alternative (or at least a cheap alternative) but never 25mm on a domestic TT, as I say I usually just use 10mm simply because I carry this size for main bonding purposes anyway.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
MAIN EARTH BONDING domestic installation
Prefix
N/A
Forum
Domestic Electrician Forum
Start date
Last reply date
Replies
32
Unsolved
--

Advert

Thread statistics

Created
piz,
Last reply from
spark 68,
Replies
32
Views
4,924

Advert

Back
Top