was called out to house earlier where couple had returned from holiday to find they had no power. on closer inspection I discovered that the main 80amp fuse had blown, no mcbs or rcds had tripped. any ideas ?
I have seen a main switch go due to the terminals in the cutout not being as tight as they should be, DNO came and rectified the fault, I got a head shake for cutting the seal.
I've had a couple of service head fuses blow, very random times as well as there was no reason for them to do so.
I agree with Murdoch, sometimes they just pop.... Get the fuse changed and job done!
Customer of mine had the main fuse blow due to a fault on a junction box this was followed by a smell of burning plastic didn't blow the consumer unit fuse
There could be a fault that has blown clear under fault conditions and taken the main fuse
At very high fault levels and a fault close to the consumer unit the main fuse could clear the fault because it takes a finite time for the contacts to move in the magnetic trip.