Hi Everyone,
Has anyone had this situation. The main incomming supply is pme which is in a isolated building all on its own.There are 3 different buildings all isolated from each other.The buildings all have water supplies/gas.I am installing 3 separate supplies to these buildings with swa & separate cpc,back to the main incomming supply. Does the main bond to gas/water have to go back to the incomming supply from each building ??? They are quite a distance apart.Any ideas welcome.Or can they be connected to the local board ??? :confused:
 
In this situation you can run bonding back to in comming supply.

However, you can also run the SWA submain to the outbuildings but not connect the cpc in the enclosure/cu. (still bond the armour at the supply end)

You then TT the outbuilding supply for your main earth and bonding.
 
Hi Everyone,
Has anyone had this situation. The main incomming supply is pme which is in a isolated building all on its own.There are 3 different buildings all isolated from each other.The buildings all have water supplies/gas.I am installing 3 separate supplies to these buildings with swa & separate cpc,back to the main incomming supply. Does the main bond to gas/water have to go back to the incomming supply from each building ??? They are quite a distance apart.Any ideas welcome.Or can they be connected to the local board ??? :confused:
Hi Coxy,
I recon that it might depend on what size is your earthing conductor/swa.If your buildings are supplied in 16mm say.I would supply a main earth terminal at each building,and take bonds to there. I don't really understand why the recomendation is to make remote buildings TT.I have problems with TT systems, zs disconnection times of mcbs cannot be met,we have to rely on rcds to disconnect the fault,and as we know
rcds are rarely tested monthly as recommended,and often go faulty.I would prefer the "sound" earth of a pme any day. But thats only me.
 
The recommendation is with regard to not having to run a separate (10mm?) bond back to the origin of the supply, which would be the case if there are services in the outbuilding.



Its only to make installation easier.


But if the supply to the outbuilding is 16mm then an MET at each board would be ok.
 
Last edited by a moderator:
Hi Thanks for the help.I have looked at the nic tech manual,and it does suggest turning installations into tt systems.However i think that the best solution is because i have run separate cpc's with the swa is to install met at the db then run water bonds back to there.The only problem would be the size - am i right in thinking that it would have to be half the size of the incomming neutral ?? reg 544.1.1
Thanks.
 
Correct, each building has to be a TT system, the earth from the incoming building must not be extended to the outbuildings. local earth rods required at each building. Page 134 of BS7671 table 54.8 will give you your bonding conductor sizes.
 

Reply to Main water bond in several buildings in the Australia area at ElectriciansForums.net

Similar Threads

We are refurbishing an empty commercial building at the minute and I don't do commercial stuff day in day out so not entirely clued up on...
Replies
11
Views
1K
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Good morning all, long time reader first time post so looking for some help I’m qualified as an electrician but haven’t worked as a sparky for...
Replies
5
Views
2K
Been looking at a CU change in a small office and would appreciate comments on the following. Office is supplied from the mains intake in the...
Replies
52
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock