Discuss Melted 13amp Spur switch in the Australia area at ElectriciansForums.net
L
luke teague
Feed a storage heater on economy 7. The 13amp spur switch for it is to the side of it wasn't working properly and the phase input looked a bit melted.
I have tested all the wiring IR is fine and so is continuity and Zs thats without the melted broken switch as it fell apart in my hands.
It felt loose as if the mechanism had come apart inside, so I took it apart to see. It hadn't come apart, but melted and feel apart. there was a hair line crack all the way up the switch.
The most melted part is the neutral supply connector, the cable covering had even melted slightly an inch or so up the cable.To me this is quite alarming, it doesn't look that far away from starting a fire.
The circuit is on a 16 amp mcb and not all that old. but even the 13amp fuse spur never blew.
I will change the switch and reposition it as its very near the heater and the heat can not help things.
I'm worried that the same thing is going to happen again, has anyone seen anything like this before, or know what could be causing it?
The storage heat tested out of and i was thinking if it was that surely the cable for the heater would be damaged instead.
Loose connection sounds like the obvious reason, but if the connections were tight then something else isn't right.
Sometimes you can have a loose connection and because of the heat build up at the connection point, the connection appears to be tight and therefore misleading.
I would check polarity throughout the circuit (including the heater) because it seems strange that the fuse/MCB did not go with this problem?
Re-test everything again, fit a new (decent quality) switch and check the loading for the circuit.
Warren
The fact you state that the neutral was the most melted part would suggest either a loose neutral connection at the termination or a weakness in the manafacured internal FCU connections.
Cheap product i reckon.
Coupled with the fact that it most likely would have been a loose connection and the terminals seized or melted with heat build up.
I have also seen badly terminated conductors where the screw has been put through the insulation instead of gripping the bare copper. This can also contribute to high resistance in the terminal.
Just replace it with a better quality product, and whilst your at it, have a check of any other heaters that are connected to similar makes of spur.
just a thought all the storage heaters ive done have NEVER been on a 13 ampspur always a 20amp double poleswitch what is the load of the heater
1 amp 250 w so 1000w or 1kw is 4amp so 3kw is 12 amp =4x3 or thier abouts for easy working out if you exceed the rating that is why you nearly had a fire
As per Bon Jovi
It should have been a 20A DP switch to supply this heater that is why it has over loaded and burnt out.
What size of wattage is the heater?
have you ever seen a flash inside a immersion heater switch when it is first switched on manually this is because when the contacts on the switch close together when it is operated just befor the gap closes a spark jumps acoss causing a flash this is why the contacts on that spur are of a certain thickness and size to be able to withstand that damage which is being done over along period of time (its lifetime ) but if you increase the load the spark is greater causing greater damage which the contacts are not designed for this is why you have to upgrade your switch to a heavier switch such as 20 amp dp switch with thicker contacts s as not to cause damage either the switch stops working or it burns out which noboby wants as regards the fuse should blow im not sure it would if its a fault it would blow but sometimes a fuse wil carry alot more load than it was designed for imm sure someone will tell us after reading this hope ths helped
Something similar has just happened to me.
See picture:
The fuse didn't blow, but the jumper lead between the fuse and switch has melted. I think its a cheap switch that can barely cope with 13amps - but surely the fuse, even though it might carry a bit more than 13amp, should blow BEFORE the switch starts to melt!
The jumper lead was preinstalled in the switch and appeared to be fitted professionally at manufacture - I confess I assumed it was and didn't check whether it has been installed correctly (i.e. insulation properly stripped) so this could be a possible cause i.e. poor connection.
This is a screwfix varilight FCU switch BTW.
I totally agree with bonjovi storage heaters as well as immersion heaters should always be on a 20 amp DP switch not a fused spur , running these items on fused spur's causes the contacts on the fuse carrier to run hot even on relativly low loads 2kw say and these are on for 7 hours econonmy 7 .then cool down heat up cool down heat up ,the connection the get weak and dont make a tight contact then eventually end up melting so if you come across this on a periodic i feel it should be a Code 1 ,i say this as the exact same thing happend on an immersion heater which had been wired into a fused spur set fire the the house luckily they faimily had smoke detectors and got out ,as the regs state protection against fire .
See picture:
Wont blow unless there is a short ,or a fault to earth, especially as its on the incomming side of the fuse
How many amps do you think caused this melting - less than needed to blow the fuse surely? I thought the point was that a serious short or earth would lead to very high currents - hence blowing the fuse. My point is the fuse should surely be the weak point, not another part of the switch!!
or overload sorry missed that one brains switched off, i was refering to load fault the melted cable wouldnt cause the fuse to blow ,but if there was a fault on the out going it should have , where the melted cable is is before the fuse so the fuse in the fcu wouldnt protect the melted cable what is protecting that would be the protective device at the CDU ,which could be a rewireable fuse whch requires greater currents to blow especially if its a 3036 30 amp suppling a ring
probably not cause by overload or current more likley to be a loose or faulty conection ,looking at the picture i was refering to and as i have stated its on the incomming side of the fuse so wouldnt blow that fuse ,not knowing where this was connected to radial or ring if it was the ring then the cable which has melted would be protected at 32 / 30 amps depending on type of protective device if its a rewireable fuse it could take 40 plus amps to blow it and as 2.5 is rated less than that its going to melt ,if you get a fault thats less than the tripping fault of the protective device and more than the cable rating
On reflection I think you're right to assume its may not be due to excess amps (>13), but perhaps it has melted at 8 amps or whatever do to this poor/loose melted connection, well before the fuse which should go at "13" amps, or thereabouts.
It looks to me as though the factory wire in the switch (it came fitted like that and neither me nor tyhe electrician who fitted it touched that part) was less able to take the ampage than the fuse - which just seems a nonsense, and unsafe.
Reply to Melted 13amp Spur switch in the Australia area at ElectriciansForums.net
Been round to a house to quote to replace some storage heaters for new panel heaters and came across a strange (to me at least) way of wiring the...
4K
Hi, So I'm trying to understand what's going on with my off-peak electricity supply, as something's wrong with it and I'm trying to determine if...
Hi, Have normal fused immersion heater switch. I would like to add a smart wifi switch to it so when my Solar is producing over 3k spare, going...
Hi all looking for a bit of advice. I've been asked to price a rewire for a early 70's build 2 bed apartment. The apartment block was built in the...