Went to see a lady to quote for removing some sockets/lights before the builders knock down a few walls. Just like to check everything.. earthing/bonding etc and noticed that the meter was still running slowly after I switched the CU off?

Slightly off subject but Its a house in the middle of a built up area with TT, why would it have TT and not TN-C-S?

Just a few odd points!!!!
 
There is still alot of TT systems running along old terraced houses on the external wall at high level but they are slowly been converted to TNCS
 
now..
you know its all about the senses in these situations dont you...
so, can you smell summat?=sense of smell
can you hear extractors goin?=sense of hearing
and if it is a grow then for christs sake dont rely on the sense of touch will you....not at some `enterprises` iv witnessed...
 
is another CU run from it via henleys?

That was my first thought but I cant see anything obvious, I'll try and put up a picture later.

There is still alot of TT systems running along old terraced houses on the external wall at high level but they are slowly been converted to TNCS

Thanks Darkwood, thats good to know.
 
now..
you know its all about the senses in these situations dont you...
so, can you smell summat?=sense of smell
can you hear extractors goin?=sense of hearing
and if it is a grow then for christs sake dont rely on the sense of touch will you....not at some `enterprises` iv witnessed...

Well you've made me smile Glen :smile5:..... got no idea what you're talking about
though :yesnod:
 
This reminds me of when I encountered a property with a separate underdwelling at the back. For thirty odd years they'd been paying for someone elses lighting and upstairs sockets!
 
You look to break through the incoming water main too, keep the ground moist, guaranteed a stable low reading.
Contrary to popular belief I did it properly mate. Dug down about a metre to make sure I wasn't going to hit anything then I started driving the rods, three rods later I decided I'd had enough.
 
Contrary to popular belief I did it properly mate. Dug down about a metre to make sure I wasn't going to hit anything then I started driving the rods, three rods later I decided I'd had enough.

Your medal from E54 is winging its way to you all the way from China as we speak. ;)
 
There is still alot of TT systems running along old terraced houses on the external wall at high level but they are slowly been converted to TNCS

Not in Cornwall. Western Power are refusing to convert overhead supplies to TNCS if not already converted/connected.
I know ENG54 will be along shortly to question this, so I'm about to fire up the scanner and scan last letter from WP to confirm.
 
I did a job last year in Devon, with the main switch off (No other loads connected via henleys etc), the meter ran backwards for about ten minutes afterward. Only slowly, but backward all the same!!!
 
Went to see a lady to quote for removing some sockets/lights before the builders knock down a few walls. Just like to check everything.. earthing/bonding etc and noticed that the meter was still running slowly after I switched the CU off?

Slightly off subject but Its a house in the middle of a built up area with TT, why would it have TT and not TN-C-S?

Just a few odd points!!!!
utter rubbish, if its disconeccted on the outgoing how the hell can it still be reading supply
 
Hate to drag things back to the original subject.

HHD with everything isolated did you use you’re clamp meter on the live tails? Don’t go on the neutral as that doesn’t register in the meter.

Tell me what you find.

Just to add, printed on the meter there will be a ratio, 1KWHr = --- rotations. Time the rotation and work out the inconsistency. But only if all the load is truly isolated.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

HappyHippyDad

Esteemed
Arms
Supporter
-
Joined
Location
Gloucestershire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
meter still runs after power off!!
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
27
Unsolved
--

Advert

Thread statistics

Created
HappyHippyDad,
Last reply from
Knobhead,
Replies
27
Views
3,090

Advert

Back
Top