• IMPORTANT: Please note that nobody on this forum should be seeking from or providing advice to those who are not competent and / or trained and qualified in their field (local laws permitting). There is a discussion thread on this global industry-wide matter HERE. This also has more information about the warning with regards to sharing electrical advice in some countries. By using this forum you do so in agreement to this.

Discuss Minor Works Cerificate question in the Electrical Forum area at ElectriciansForums.net

Welcome to ElectriciansForums.net - The American Electrical Advice Forum
Head straight to the main forums to chat by click here:   American Electrical Advice Forum

Reaction score
17
Hi Folks,

I am filling out a minor works certificate for 2 fused spurs I have fitted from 2 socket in the livin room to supply 2 wall lights 5A fuse fitted in spur.

My question is on the minor works cert where it says Method of fault protection, do I put Automatic disconnection of supply??

And for protective device fo the modified circuit Type BS1362 Rating 5A??

Thanks in advance

Dan
 
it will be ADS and protective device will be the upstream rating on that circuit i.e. MCB rating in CU
not your 1362 fuse for the wall lights.
 