codger

~
Sep 14, 2008
61
12
83
United Kingdom
Morning. A friend and I have been carrying out some EICRs on properties in our area. Recently, my mate has come across two houses in which the lighting circuits do not have any earthing at all. They have been run in twin and earth but the earths have all been snipped off at lighting points, switches, jointboxes etc. The colours of the cable are black and red (give you an idea of the age of the installation). The ceiling, floors and walls are all concrete and it looks like the twin and earths have been dropped down conduit drops to the switches.

As far as the EICR goes what would you put this down as...? We're thinking C2. Someone else suggested that it goes down as a C3 as long as it's stipulated that only plastic fittings should be used.

Cheers
 
The cpcs should be terminated but the Coding would depend upon if any back boxes, accessories or fittings need the connection of a cpc for fault protection. Are they metal back boxes and if so do they incorporate nylon fixing lugs because they don't need earthing. If they have cut them out sounds like a rough job.
 
The cpcs should be terminated but the Coding would depend upon if any back boxes, accessories or fittings need the connection of a cpc for fault protection. Are they metal back boxes and if so do they incorporate nylon fixing lugs because they don't need earthing. If they have cut them out sounds like a rough job.

They are metal boxes....no plastic inserts though. I know the ones you mean. We've peered up at a switch and spotted that it looks like the old conduit system....the ones where the switch back boxes had a wee spigot that pushed onto the end of the conduit drop.
 
Yes mate. No sign of the conduits at the consumer unit. Just three twin and earths floating away into the wall at the board.
There isn't an existing board behind it fitted flush is there where these conduits maybe terminated.
 
  • Like
Reactions: Hellmooth
c2 mate, unless there is absolutely no metal fittings, backboxes, conduit etc.
Was going to comment but forgot what is was:astonished:
 
  • Like
Reactions: Vortigern

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
United Kingdom

Thread Information

Title
Missing cpc in domestic lighting circuit
Prefix
N/A
Forum
Domestic Electrician Forum
Start date
Last reply date
Replies
11
Unsolved
--

Advert

Thread statistics

Created
codger,
Last reply from
The Ghost,
Replies
11
Views
3,680

Advert