Discuss Neutral / earth fault in the UK Electrical Forum area at ElectriciansForums.net
had this yesterday on a TN-S. both RCDs failed to trip on test button and with MFT. found the cable responsible and dissed it, both RCDs now tripping fine. further investigation next week as 1. the cable is short and disappears behind meter board. 2. no idea what the cable feeds as nothing seems to have stopped working.
it`l be for a bypass...
RCD will only trip if there's current flowing down to earth. If there's no load on the RCD it won't trip. Other option is that it's faulty, if you ramp test it you'll know for sure.
Are you asking why an RCD won't trip when you have Earth-Neutral link at incomer (as per PME/TNCS)?
If so this is because the RCD only monitors the circuit it is protecting (on the load side of the unit)
There is plenty of literature etc around explaining in detail how RCDs work - if you are in training it's worth a look.
If I misunderstood your question then ignore!
It's like why dies it keep tripping when applying a load... But you have got the grey as the earth instead of neutral......, I know
Reply to Neutral / earth fault in the UK Electrical Forum area at ElectriciansForums.net
Hi all, Hope you're keeping well I'm currently wiring a small commercial premises. 3 phas incoming supply, 16sq cables As it is in an urban...
Hi was recently at a property and was installing a Solar PV system. was doing my testing and i came across a weird result when doing the...
Evening all, I had a quick Friday afternoon domestic job that has turned into a PITA and I'd appreciate your help. While adding some new lights...
I'm in a questions asking mood tonight. I briefely looked at a job today and I need to recommend a board change but need to justify it. Firstly...