What exactly are the neutral leads for? and if a neutral to earth happened on a board with just RCBO'S in it, why doesnt the fault travel along that neutral and affect the other RCBO's?
In that instance both will trip.
Hope you can see the fault direction arrows on the last drawing
Correct.As far as I understand it, if there is an N/E fault on RCBO1 and RCBO2 shares a neutral on the load side then RCBO2 will also see an Earth fault and so it will trip.
Correct.
A borrowed neutral N-E fault will trip both because both neutrals (or shared one) will be connected to earth.
Just to point out that single-module RCBOs are only single-pole switches.
No. Not the ones normally in CUs.
It's not.
That's why it trips when you touch N and E.
No. It's not isolated.
So, if borrowed or connected to another neutral it will divert current from the second RCBO.
Yes...
Yes, because the current is going out through one RCBO and (some of it) back through another - so imbalance.So just to clear this up for the single pole RCBO, in relation to the drawing on page 3- bearing in mind they are single pole RCBO's instead, when we have just a borrowed neutral on RCBO 1 & 2, It will trip both RCBO,
Yes, probably at the same time if lamps on both circuits turned on.when RCBO 1 trips the current will go down through RCBO 1 neutral cable, through the RCBO1 neutral lead and trip RCBO 2 as well yea??
Not sure if you meant now or not.and when we have the borrowed Neutral and neutral to earth fault on RCBO1 it will trip RCBO1 and will it no affect all the other RCBO's as well now??? as the neutral is not isolated from the rest of them??
Yes, probably at the same time if lamps on both circuits turned on.
It's easier to see if you draw the circuit and follow the current path(s).
So the current wont travel back up the supply side of an rcbo then?
Not sure if you meant now or not.
Don't forget that an N-E fault will only trip the RCBO whose neutral has faulted to earth and the one whose neutral is connected to the neutral of the first - not any others because the fault is on the load side and load side neutrals are not connected (except in these fault conditions).
Yes, as no other circuits are connected to it (unless by these faults) none of the other RCBOs will be affected.
Yes.
The term 'Borrowed Neutral' is a bit misleading. Think of it like this -
The first RCBO has a borrowed Neutral from the second RCBO, and...
...the second RCBO has a borrowed Live from the first RCBO so both will have an imbalance.
As I said, if you draw it, it becomes a lot easier to see.
ive PM you and should have explained i was refering to DP rcbo's only you will appreciate throwing a single pole in the mix would have made your confusion worse, but should have gone that route first, it just habit on my part as its what i fit in my control panels but yes domestic is usually single pole.
ive PM you and should have explained i was refering to DP rcbo's only you will appreciate throwing a single pole in the mix would have made your confusion worse, but should have gone that route first, it just habit on my part as its what i fit in my control panels but yes domestic is usually single pole.
Just now, remember and will add to this thread too for other to remember; in a tns and tncs the neutral and earth bar will be linked together if the main switch is on due to the center tap in transformer (tns) and the combined N/E in the cutout on tncs.I replied to your last PM darkwood, I dont have anything back in return? you sure you sent it ? :/
Just now, remember and will add to this thread too for other to remember; in a tns and tncs the neutral and earth bar will be linked together if the main switch is on due to the center tap in transformer (tns) and the combined N/E in the cutout on tncs.
So it shows that an E/N fault feeding back to the E and N bar through 1 or more rcbo's will not effect other rcbo's that are clear of this fault as its not on their load side.
because the neutral from the circuit being fed from the RCBO has to go through the RCBO before it gets to the neutral bar vie the RCBOs neutral lead.....so any imballances due to fault between neutral-earth are seperated from the other RCBOs/RCDs within the install....unless in series of course
This is the way I see it after having a readIs this the case with SP RCBO's as although they supervise the load side N and L they only operate the L phase. In the ideal sittuation each circuit would have its own dedicated earth however if the neutrals are linked at the supply side then where is the break in the circuit in the case of an N-E fault. I would have though an imbalance in current flowing in the faulty neutral wire would also be detected on other RCD's or RCBO's. Clarification on this would be appreciated. The regs seem to explain that a main switch isolator can be used with a seperate RCBO for each circuit but I am unsure if they mean SP or DP RCBO's. DP being mega expensive so quite reluctant to buy these even though I only have 4 ways going out on my current fuse box. Any clarification on this would be much appreciated. Hello to everyone on the forum btw.
Regards
Steve
This is the way I see it after having a read
I think the rcbo, whether single pole -n or double pole,both will disconnect both poles
However, in the single pole rcbos,the live is the rated contacts
The neutrals are not for breaking the load,they operate after the live so do not switch the loads
Hence the neutral tail used, so that it isn't confused with the live terminal
The double pole rcbo has both poles monitored and rated, so no need for the neutral tail, both poles disconnect
In the case of a neutral/earth fault current could flow from the neutral bar through the RCBO to earth through the fault - in which case the RCBO will trip. None of the other RCBOs should trip because there isn't a path to earth through the neutrals of the other circuits. Remember the neutral busbar is 'down wind' of the other RCBOs.Is this the case with SP RCBO's as although they supervise the load side N and L they only operate the L phase. In the ideal sittuation each circuit would have its own dedicated earth however if the neutrals are linked at the supply side then where is the break in the circuit in the case of an N-E fault. I would have though an imbalance in current flowing in the faulty neutral wire would also be detected on other RCD's or RCBO's. Clarification on this would be appreciated. The regs seem to explain that a main switch isolator can be used with a seperate RCBO for each circuit but I am unsure if they mean SP or DP RCBO's. DP being mega expensive so quite reluctant to buy these even though I only have 4 ways going out on my current fuse box. Any clarification on this would be much appreciated. Hello to everyone on the forum btw.