DB not connected directly to the main supply.
The confusing bit, characteristics at this DB, is this still related to the Distribution circuit.
You can actually read it both ways, I’ve been entering the Distribution circuit but now have my doubts.75F9686E-7EA8-4BD6-A0E4-2DAE14CC9087.jpeg
 
You've been doing it right. It's the Zs and PFC of the distribution circuit as measured at far end (the sub-main consumer unit)
This then gives you the base-line if you want to fabricate calculate Zs readings from the R1+R2 readings of the final circuits.
 
It's self explanatory. You're selecting an existing DB, then a sub DB, then entering the details for the sub DB and then the test results at it.
A distribution circuit is feeding the sub and needs listing as an out going circuit from the main DB.
Hope it helps.
 
Last edited:

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

cliffed

Arms
-
Joined
Location
Worcester
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Niceic certification
Prefix
N/A
Forum
Certification NICEIC, NAPIT, Stroma, BECSA Forum
Start date
Last reply date
Replies
4

Thread Tags

Advert

Thread statistics

Created
cliffed,
Last reply from
cliffed,
Replies
4
Views
1,407

Advert

Back
Top