buttonmoon

Hello

I was just trying to test a very old Simplex 3 phase DB which I found in the basement boiler room of a small office block. The door was hanging off... ok I can fix that, there are several holes knocked out of the base of the metal case.... again that shouldn't cause too much trouble, one live wire dangling across the top of the box...... traced it to a twin socket in a cupboard and disconnected it. Right now lets isolate the thing and have a proper look....ah, no main switch, just four cables going straight to four bars (including the neutral). I think it's being fed from an isolator upstairs. Does it not need to have a local means of isolation, as in, in the same room?

any thoughts??
 
What you have there is a simple Distribution board (Definitions Section 2 of the Regs) As it seems you doing a PIR then no code. If the upstairs switch isolator is not marked identifying this DB, and the panel cover of the DB is not marked identifying the switch isolator and it's location, then I would code it a 4. Again if there is no board schematic or anything linking the switch isolator/DB, ie drawings, panel schedule etc, then again a code 4

I'm sure you will find loads of these type of boards dotted around commercial/industrial premises, I know they were prevalent on older installations.
 
Last edited by a moderator:

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
No main switch
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
3

Advert

Thread statistics

Created
buttonmoon,
Last reply from
IQ Electrical,
Replies
3
Views
1,949

Advert

Back
Top