Discuss Nuisance tripping after splitting a ring main in the UK Electrical Forum area at ElectriciansForums.net
How many sockets in kitchen? Might be worth disconnecting them all one by one. Be quicker in long run probably.
Tut, tut....kitchen faults. OP's head 'll be spinning. Start from scratch. Check at all sockets for direct spurs or even JB's behind units. Disconnect all sockets and FCU's...(neons). Test each leg after each disconnection. You don't mention any continuity testing.
Anything outside any external sockets or flood lights?
from short leg which we believe goes straight back to the board we are getting continuity on the L and E
When you say continuity, do you mean end to end on the cores or from one to another?
And what about the neutral?
I would do IR tests from both "ends" of the leg .............
what were the R2 readings for each of the L, N and CPC before you took the ring apart?
from one another
neutral to earth ok
neutral to live ok
only getting it on live to earth
from one to another
fair point
but at this time of night i'm not even sure what my own name is any more
but we are going through the slow process of taking sockets apart and testing
Who is “we”?
Basic rules of fault finding
Continuity of all cores
Ir of all cores
Split circuit
Repeat above
If you don’t confirm end to end continuity of the cores, you will go round in circles
Your original post said 5 double sockets didn't it? Where are the extra 3 to make 8?
Maybe its time to call it a day. Fault finding takes years of experience to master. Why not be honest to your friend and say its above your level. Nothing wrong with knowing your limits and holding your hands up to admit it. Get the guy to get an experienced sparky in to locate the fault and explain where and how he located it. Use this as a opportunity to learn.
Reply to Nuisance tripping after splitting a ring main in the UK Electrical Forum area at ElectriciansForums.net
Essentially I have a "normal" socket in a ring mains, i.e. one 2.5mm T&E going in and one 2.5mm T&E going out. I am looking to simply add two more...
Ring main was on a c40 rcbo so I tested the circuit everything was fine and dropped down onto a b32, It’s quite a long circuit but only serves...
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Hi all, we had our gas hob removed months ago and finally just got round to putting an induction hob in. Its a normal 4 ring induction but one of...