Hi - it might just be worth repeating IR at 250V to be sure you are not looking into some surge arrestor somewhere.
no difference there
latest is we seemed to have found the first socket from the long leg
we have continuity on L-L
N-N
but no earth
But new headache is that if we energise circuit with only the Live connected it still trips the RCD
 
Maybe its time to call it a day. Fault finding takes years of experience to master. Why not be honest to your friend and say its above your level. Nothing wrong with knowing your limits and holding your hands up to admit it. Get the guy to get an experienced sparky in to locate the fault and explain where and how he located it. Use this as a opportunity to learn.
appreciate what you are saying but how am I going to learn if I give up at every problem I encounter
 
Thanks everyone for you help and advice
we still have an earth fault when we are getting 240v across earth-netrual
now on both legs.
which is the part we cannot get our heads round as this circuit has been fine up until last week. and nothing has been added or any work carried out.
we are in the proccess of reconnecting all the sockets back up and i will keep everyone inform of what the problem is when we finally get it sorted
 
latest update
it now seems that we have L-E fault on both legs ?
I'm getting a reading coming back through the Earth on both legs

As you're going round breaking the circuit into legs are you putting the conductors into chocblocks or similar to keep them separate or are you just letting the conductors float free to touch each other or the backbox?

Thanks everyone for you help and advice
we still have an earth fault when we are getting 240v across earth-netrual
now on both legs.
which is the part we cannot get our heads round as this circuit has been fine up until last week. and nothing has been added or any work carried out.
we are in the proccess of reconnecting all the sockets back up and i will keep everyone inform of what the problem is when we finally get it sorted

You can't just go around reconnecting and re-energising when you have faults still on the circuit. If it doesn't pass the dead tests you don't proceed to live tests. 240V between neutral and earth suggests you've lost your neutral or earth and isn't safe. Lock the circuit off until you can go back with a clear head and work through methodically or someone else can come to fix it for you.
 
I had a similar scenario at a mate's house last month: he'd been changing switches, and got intermediates, two-ways and singles completely messed up, and had mixed up two separate multi-way lighting circuits in the same enclosures. Nothing made sense: the behavior of his lighting was hilarious.
With multiple concurrent faults there's sometimes too much going on to hold the logic in your head.
In that case I find the best way is to STOP. To give up trying to be clever and to disconnect EVERYTHING. All accessories off, all cables neatly disconnected. Then get pen and paper, a long flying lead and trace the exact route of every cable. Draw it as you go. Then do continuity and IR on all sections, logically and consistently.
It's then a great feeling when the 'A-Ha!' point is reached, which it will be.
Good luck :)
 
I had a similar scenario at a mate's house last month: he'd been changing switches, and got intermediates, two-ways and singles completely messed up, and had mixed up two separate multi-way lighting circuits in the same enclosures. Nothing made sense: the behavior of his lighting was hilarious.
With multiple concurrent faults there's sometimes too much going on to hold the logic in your head.
In that case I find the best way is to STOP. To give up trying to be clever and to disconnect EVERYTHING. All accessories off, all cables neatly disconnected. Then get pen and paper, a long flying lead and trace the exact route of every cable. Draw it as you go. Then do continuity and IR on all sections, logically and consistently.
It's then a great feeling when the 'A-Ha!' point is reached, which it will be.
Good luck :)
Cheers for that
as we can not find out why we have 240v coming down the earth on both legs
we have run a temp 2.5mm T&E replaced 32 amp with 20 amp MCB so that the kitchen is working and safe.
tomorrow is another day
 
ps: What kind of test instrument/s do you have?

I have a sneaking suspicion you may be working with a cheap multimeter, may be touching the probes when taking readings (this is especially a problem if it's an auto-ranging model) or are diagnosing 'short circuits' between cores by energising one then testing the other with a neon screwdriver or volt stick.

Any of the above is not only dangerous but a waste of time which will take you round in circles with false positives.

Apologies if I guessed wrongly ... :)
 
An interesting and novel use of the word 'safe' :)
I thought so
but as we have no ring and we have established where each leg comes into the kitchen. We have established that round the kitchen is ok. so turned it into a radiul and downsized the MCB for the moment.
it will be something simple as we can not see a mouse chewing though both legs under the floor
 
... we can not see a mouse chewing though both legs under the floor
Mice love T&E. Or at least in my area (Norfolk) they do.

I tempt them with the finest parmesan, and peanut butter, but still - and despite being considered not unintelligent creatures - they prefer to eat the wiring.

I wouldn't be in the least surprised, if you have mice, that you will find multiple horrors which might well explain everything.
 

Reply to Nuisance tripping after splitting a ring main in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Essentially I have a "normal" socket in a ring mains, i.e. one 2.5mm T&E going in and one 2.5mm T&E going out. I am looking to simply add two more...
Replies
2
Views
278
Ring main was on a c40 rcbo so I tested the circuit everything was fine and dropped down onto a b32, It’s quite a long circuit but only serves...
Replies
26
Views
2K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
778
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi all, we had our gas hob removed months ago and finally just got round to putting an induction hob in. Its a normal 4 ring induction but one of...
Replies
3
Views
783

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock