Megger lighting circuit. L-e short found cable its the switch wire for outside light.
Opened fitting no water present.
Disconnected fitting it clears. The cable is not shorting to the plate or any kind of pressure fault
If i disconnect light it clears.
Its a bulkhead fitting with 2 8w florescent lamps.
With power on and switch off circuit is fine. Turn switch on it trips.
Help please