Innominata

Hi All,
I am adding new sockets,switches and light fittings to a refitted industrial unit.The original 3 phase. board is about 40years old with cartridge fuses.Is there any problem installing a new single phase board for the new circuits via a 63amp cartridge fuse from the old board.Also the existing lights have been spurred off the old power radial supply,do the new lights have to be on their own circuit or can i spur off from either a new ring or the old power radial as it is now.Many thanks
 
Hi All,
I am adding new sockets,switches and light fittings to a refitted industrial unit.The original 3 phase. board is about 40years old with cartridge fuses.Is there any problem installing a new single phase board for the new circuits via a 63amp cartridge fuse from the old board.Also the existing lights have been spurred off the old power radial supply,do the new lights have to be on their own circuit or can i spur off from either a new ring or the old power radial as it is now.Many thanks

Are you sure the fuse carriers will take the 63 amps you require? they have their rating stamped on the top, if that is ok then yes you can install a single phase board.

As for the lights, it doesn't make any difference if you are correct on loadings etc etc but I would have thought you would be much better to install a new circuit from the dis board
 

Reply to Partial rewire of industrial unit in the Australia area at ElectriciansForums.net

Similar Threads

I have been asked to change cu from old fuse board which has 6 fuses. Only 4 fuses are used. The first fuse feeds cooker circuit. This is not used...
Replies
17
Views
809
In a property with two consumer units one for the ring main etc., and the other for the 1970s storage heaters (storage heater CU looks like it’s...
Replies
14
Views
1K
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
Hello, I am hoping this is in the correct forum. To start, I acquired a film processing machine that runs on 3 phase. Now before getting the...
Replies
19
Views
3K
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock