Discuss PAT testing a Ariston Andris under sink water heater in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net
punkin
Hi All
I’ve come across this heater Ariston Andris Lux Undersink Water Heater 2kW 10Ltr - Screwfix - https://www.NoLinkingToThis/p/ariston-andris-lux-undersink-water-heater-2kw-10ltr/3248g
Its a plugin & I’m trying to PAT test it.
It doesn’t say which class its is under (1 or 2) I would assume it’s a class 1 but when I try the Earth continuity to the pipes going in and out, I get a fail, no continuity to earth whatsoever
Does anyone know if its Class 1 or 2?
Pete
Ariston undersink water heaters (usually / should) have these fitted at the inlet and outlet.
The manual I just found on the Internet shows a requirement for a 3 core supply cable and an earth connection when installing it. Not 100% sure it was exactly the same version though. If the device doesn't have the class II logo on the spec plate then it will not be double insulated and so will be class I.
As per DPG, I found by accident an installation manual for the South African model (the wording of the instructions being very similar to the European one except for standards) which has a diagram showing the earth being connected to the metalwork of the immersion heater mounting bracket Inside the unit.
It would seem that to test earth continuity you would have to take the cover off!
Hi All
Pete
No bonding to the I assume copper water pipes ?
The instructions require you to install the isolating plumbing fittings (post #2) to avoid electrolytic corrosion of the unit!
But yes, I agree, if the pipes are copper and bonded and the unit is connected up you would expect the earth continuity. But that's not a PAT, sorry ITSEE, test!
I'm surprised no-one has yet asked the obvious question..... why are you trying to test a non-portable device with a PAT test?
Don't forget it's ISITEE, not PAT. It can apply to non portable items as well. And often doesn't involve actual testing. The term PAT is very misleading.
True - however - that's not what the OP stated.
PAT testing is no longer a recognised term.
The Code of Practice edition 5 removed all traces of the term.
And that's for precisely the reason raised by @Rockingit, that is, to remove any confusion between what equipment should be tested and/or inspected. ISITEE applies to ALL electrical equipment whether portable or not.
Yes I would have thought so but the fittings on this are slightly corroded. So I would assume the outlet would be insulated like in a shower. I will have to open the thing I reckon for a closer look.
Yep I think I would agree with you, bugger, as you can imagine, I need to disconnect the pipes under the sink and I'm not as flexible as I used to be.
Reply to PAT testing a Ariston Andris under sink water heater in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net
Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
Hi, would would be your thoughts on this one? On the floor under the sink in my kitchen is a power cord that connects the small undersink water...
I've been asked to provide hot water in a small kitchen, no room for a storage tank, any recommendations on under sink heaters? The largest demand...
We have started a business building garden rooms/caravans/mobile homes under the caravan act. We have only done one so far and I got an...
Hi can anyone recommend an instant water heater for an ensuite hand basin. I'm after recommendations of products that people have fitted/ used...