Ariston undersink water heaters (usually / should) have these fitted at the inlet and outlet.
 

Attachments

  • Ariston.PNG
    Ariston.PNG
    238.1 KB · Views: 4
The manual I just found on the Internet shows a requirement for a 3 core supply cable and an earth connection when installing it. Not 100% sure it was exactly the same version though. If the device doesn't have the class II logo on the spec plate then it will not be double insulated and so will be class I.
 
As per DPG, I found by accident an installation manual for the South African model (the wording of the instructions being very similar to the European one except for standards) which has a diagram showing the earth being connected to the metalwork of the immersion heater mounting bracket Inside the unit.
It would seem that to test earth continuity you would have to take the cover off!

A60F4D66-96F0-44AE-B35E-AA1D8BFB24CC.jpeg
 
Last edited:
  • Like
Reactions: DPG
Hi All

I’ve come across this heater Ariston Andris Lux Undersink Water Heater 2kW 10Ltr - Screwfix - https://www.screwfix.com/p/ariston-andris-lux-undersink-water-heater-2kw-10ltr/3248g
Its a plugin & I’m trying to PAT test it.
It doesn’t say which class its is under (1 or 2) I would assume it’s a class 1 but when I try the Earth continuity to the pipes going in and out, I get a fail, no continuity to earth whatsoever
Does anyone know if its Class 1 or 2?

Thanks
Pete
No bonding to the I assume copper water pipes ?
 
No bonding to the I assume copper water pipes ?
The instructions require you to install the isolating plumbing fittings (post #2) to avoid electrolytic corrosion of the unit!

But yes, I agree, if the pipes are copper and bonded and the unit is connected up you would expect the earth continuity. But that's not a PAT, sorry ITSEE, test!
 
Last edited:
  • Like
Reactions: punkin
I'm surprised no-one has yet asked the obvious question..... why are you trying to test a non-portable device with a PAT test?
 
  • Like
Reactions: Resu
I'm surprised no-one has yet asked the obvious question..... why are you trying to test a non-portable device with a PAT test?

Don't forget it's ISITEE, not PAT. It can apply to non portable items as well. And often doesn't involve actual testing. The term PAT is very misleading.
 
  • Like
Reactions: punkin and mainline
Don't forget it's ISITEE, not PAT. It can apply to non portable items as well. And often doesn't involve actual testing. The term PAT is very misleading.
True - however - that's not what the OP stated.
 
PAT testing is no longer a recognised term.
The Code of Practice edition 5 removed all traces of the term.
And that's for precisely the reason raised by @Rockingit, that is, to remove any confusion between what equipment should be tested and/or inspected. ISITEE applies to ALL electrical equipment whether portable or not.
 
Anyone testing equipment for safe use, should also be competent enough to be able to ensure that the supply is also safe.
 
  • Like
Reactions: Avo Mk8 and loz2754
Ariston undersink water heaters (usually / should) have these fitted at the inlet and outlet.
Yes I would have thought so but the fittings on this are slightly corroded. So I would assume the outlet would be insulated like in a shower. I will have to open the thing I reckon for a closer look.
 
As per DPG, I found by accident an installation manual for the South African model (the wording of the instructions being very similar to the European one except for standards) which has a diagram showing the earth being connected to the metalwork of the immersion heater mounting bracket Inside the unit.
It would seem that to test earth continuity you would have to take the cover off!

View attachment 107896
Yep I think I would agree with you, bugger, as you can imagine, I need to disconnect the pipes under the sink and I'm not as flexible as I used to be.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
sheffield

Thread Information

Title
PAT testing a Ariston Andris under sink water heater
Prefix
N/A
Forum
Electrical Testing & PAT Testing Forum
Start date
Last reply date
Replies
14

Advert

Thread statistics

Created
punkin,
Last reply from
punkin,
Replies
14
Views
3,436

Advert