your a fool.
it wont pull 100kw.
a 100a main switch is rated for around 23kw.
what makes you think you will pull as much power as lite industry?
dont forget if you need this much power you will need your own transformer and an 11/33kv supply lol
your calculations are way off
thats where you are wrong ...... the equipment is above ground..... the pool is below ground meaning itll need more 'power' to pump the water up
3 x 24KW heating pumps...... 72KW
2 x 3KW filter pumps...... 6KW Krystal Clear Pump and Filter Set 0.95hp pump with 7.9m3 per hour flow rate - Model 3 [Krystal Clear Pump Filter Model3] - £345.00 :
1 x water treatment monitor 3KW
5 x dehumidifiers 9KW Meaco 800i Range Pool Dehumidifiers [Meaco 800i] - £3,633.27 :
There's something called diversity, it's there to take account of the fact that not all appliances will be running at full power at any one time. For example, the heaters will not be running maxed out once the pool is up to temperature, so there's an adjustment to the consumption straight away.
i think all this can be sorted by asking everyone to think it through..... i think it CAN be achieved.... BUUUUT <-- cant make it any bigger :/ sorry guys
technology hasnt get achieved the clue to it
you never know with his cold fusion and our noggin's we may just be the first people to achieve space travel.... oh wait thats been done.... damn...... ok..... interstellar space travel and the ability to go faster than the speed of light.... honestly, its not that it CANT be done its just you have to believe there is a way it CAN
In which case, perhaps you'd better delay building this house and pool until technology has caught up with your requirements. I think you'll be in for a long wait.
AT PRESENT, there is no way to make anything which is 100% efficient, let alone 500%. You can't fit a quart into a pint pot, nor can you get a quart out of a pint pot.
Sorry but there is no way to change the laws of physics. Not yet anyway.
true they lose power 'generating' power but the power that is lost isnt MORE than whats available to use
1% loss isn't sufficient to cause the motor to be under-powered and over time cause it to stop
2 MegaWatts minus 1% leaves 1.8 MegaWatts left over. if the motor demands 0.3 MegaWatts to power the generator and the demand from the house is around 1MegaWatts then there is still 0.5MegaWatts unaccounted for.... that's the question..... yes i am a pain in the :censored: and stubborn till i can understand the answer in my own mind.... so please stick with me
Basic sums, pal........2 minus 10% leaves 1.8
Sorry but there is no way to Ye cannae change the laws of physics. Not yet anyway.
Get it right Trev!
When we're trying to get you to understand that efficiency greater than 100% is nonsense, the difference between 1% and 10% is not worth mentioning.
what your saying is that the generator will ALWAYS generate 1% less than whats needed? even when the load is less than its MAX load capacity (500KW capacity ~ 100KW demand.... 99KW supplied)
No, it will generate what is needed to power the load connected to it as long as that load is less than its max output.
The power input required will always be higher than the power output for any given load.
The difference will be relative to its %efficiency.
Phasing nightmare
Thread Tags
Tags Tags
None
Michael Smith,
Dan,