Done another practice EICR form this week, and i'm a bit stumped on the reference method box on the schedule of circuits.

Is it acceptable to write LIM in the box, as i have listed in the limitations box that i am not removing floor boards/inspecting cables in concealed locations. So how could i possibly know the reference method?
 
take your best guess with the cable routing that you can ascertain.
i've never needed to record LIM for ref method.
no one expects hard and fast guarantees from an inspection , which is why the exemptions to hidden wiring is automatically printed on the 1st page of an eicr cert
and as its a domestic 90% of it will usually be clipped direct anyway.
 
Thanks biff, i had initially written reference method B however i then started to second guess myself and convinved myself that you should never 'assume' anything on a test cert so opted for LIM!

Thanks for the reply
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
PIR/EICR Reference Method Limitation?
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
2

Advert

Thread statistics

Created
Tidy Max,
Last reply from
Tidy Max,
Replies
2
Views
3,614

Advert

Back
Top