Hi,
I am having a plug & Play hottub delivered I have a double socket outside on garage wall, I need about 5m of cable to reach tub, can anyone advise on what I need to buy to get this installed I.e. socket ,cabling, rcd protection.it says I need 13amp 240v power supply.
Many thanks Nick
extension lead, but make sure it's a quality 1.5mm cable lead. use fully unwound. itit's a plug and play, just plug into your external socket.the spa should have a 10mA RCD built into it's lead.
Plug & Play be buggered! It is external to the building, so should have its own earthing system, ie its own earth rod, consumer unit, & RCD protection, all fully tested & certified. How can anyone possibly send out something which is plug & play when they have no idea what the local conditions are like!? If your going to sit in a bucket of water which is connected to the mains, you want to be bloody sure your properly protected.
Why would it want its own consumer unit?
And, as above, they often have a 10mA RCD built in.
A lawnmower could also be described as plug and play, but I’d rather be sitting in a hot tub with its 10mA in line rcd than pushing my qualcast over its own flex with no rcd.
I always use an earth stake, and move it across a couple of feet every time I change direction with the mower.
I would check your outside sockets already have a working RCD for protection. That might be in your home's CU (consumer unit = fuse box) and it ought to have a 'test' button that simulates a fault to verify it trips OK.
Then what @telectrix said about a proper extension lead.
There is a whole extra point of contention about a hot-tub being similar to a swimming pool that is a "special area" which has additional restrictions in terms of how the supply earth is delivered, etc. I would like to think that a "plug and play" tub has allowed for that in its design, so is basically double-insulated.
If not it is a bit of plug and pray!
If you recall my thread on this subject, the Lazy Spa web site did suggest Class2, but in actual fact they are Class1.
It would be interesting to know what make this hot tub is @nickcarter68 ?
The mower is 'mobile equipment' and as such should be supplied from a socket suitable for such ie has RCD protection. The hot tub is not mobile & is outside the equipotential zone of the supplying building, so therefore should be treated in exactly the same way as say a remote garage or any other detached building - ie should be provided with its own equipotential zone.
Not necessarily, and in many cases an external building can be safely connected to the house earthing arrangements, whether TNS, TNC-S or TT.
Garages do NOT have to be made TT.
this bit concerns TNC-S:
Hot Tubs and TN-C-S Supplies The NICEIC Technical Helpline is often asked whether a hot tub installed outdoors may be supplied from a circuit taken from an installation forming part of a TN-C-S system, often referred to as a PME Supply. Neither the Electricity Safety, Quality and Continuity Regulations nor the guidance given in Engineering Recommendation G12/4 – Requirements for the Application of Protective Multiple Earthing to Low Voltage Networks published by the Energy Networks Association places any restrictions in respect of the connection of a hot tub to a PME supply. G12/4 does offer several alternatives in respect of the connection of a swimming pool to a PME supply and it is sometimes suggested, erroneously, that hot tubs should be treated in the same manner as a swimming pool. However, it is clear that hot tubs fall outside of the scope of Section 702 of BS 7671 (see Regulation 702.11). So, unless, as stated previously in this article, a hot tub outdoors is installed within the zones of a swimming pool, only the general rules of that standard are applicable.
I can back it up because I am almost the only person who does things correctly, safely, and then applies all the belts and braces - my customers use me because I work on these principles and almost no-one else does.
Bit of homework needed.
not to mention that by TT earthing the bugger, you are then relying on the RCD for fault protection unless you can achieve a sub 1 ohm Ra.
You seem to have very strong opinions but I must point out the term Earthed Equipotential Zone has not been used in BS7671 for a long time.
They do if you are detached AND you are a proper electrician.
This is a bit strong and it is not that clear cut there are so many factors to take into account, you can't just say every single outbuilding needs to be TT (what if that outbuilding is a granny annexe constructed in exactly the same way as the house ? , if PME is ok for the house why not the granny annexe outbuilding). I have supplied PME earth to a garage and bonded extraneous conductive parts (I would have preferred to TT it myself but it was impossible to get enough separation distance between a TT rod and buried bonded PME metalwork, in effect rendering the whole point of making it TT pointless (and if anything making it slightly less safe by losing the low impedance earth). An opposite scenario is an insulated timber shed with an office inside it which could kept the PME earth but there are some extraneous conductive parts (water pipe, etc) imagine the run is about 150m and the SWA is already in the ground when you arrive, it would be a pain to get a 10mm in the ground to bond that pipe so TT could be a way to go (iv had a similar situation)
Some electricians might have experienced an unbelievably high number of RCDs failing & never a PEN fault so would avoid TT as much as possible, another electrician might not have come across a single failed RCD (unlikely) but experienced a lot of PEN faults so would avoid PME, everyone has there reasons for doing thing one way or another but they are still proper electricians striving to do things safely (for the most part!)
If this was my house and my hot tub, If possible I would probably make it TT and have a delayed 100ma RCD for fault protection and a 30ma RCD for additional protection, so there are 2 RCDs protecting it (if one should fail) and then I have not got the risks associated with PEN faults,
but that's just me, I don't like TN-C-S very much as an earthing arrangement as a few people on here would probably tell you.