Discuss Plug & Play hot tub installation in the UK Electrical Forum area at ElectriciansForums.net

I can back it up because I am almost the only person who does things correctly, safely, and then applies all the belts and braces - my customers use me because I work on these principles and almost no-one else does.

They do if you are detached AND you are a proper electrician.
This is a bit strong and it is not that clear cut there are so many factors to take into account, you can't just say every single outbuilding needs to be TT (what if that outbuilding is a granny annexe constructed in exactly the same way as the house ? , if PME is ok for the house why not the granny annexe outbuilding). I have supplied PME earth to a garage and bonded extraneous conductive parts (I would have preferred to TT it myself but it was impossible to get enough separation distance between a TT rod and buried bonded PME metalwork, in effect rendering the whole point of making it TT pointless (and if anything making it slightly less safe by losing the low impedance earth). An opposite scenario is an insulated timber shed with an office inside it which could kept the PME earth but there are some extraneous conductive parts (water pipe, etc) imagine the run is about 150m and the SWA is already in the ground when you arrive, it would be a pain to get a 10mm in the ground to bond that pipe so TT could be a way to go (iv had a similar situation)

Some electricians might have experienced an unbelievably high number of RCDs failing & never a PEN fault so would avoid TT as much as possible, another electrician might not have come across a single failed RCD (unlikely) but experienced a lot of PEN faults so would avoid PME, everyone has there reasons for doing thing one way or another but they are still proper electricians striving to do things safely (for the most part!)

If this was my house and my hot tub, If possible I would probably make it TT and have a delayed 100ma RCD for fault protection and a 30ma RCD for additional protection, so there are 2 RCDs protecting it (if one should fail) and then I have not got the risks associated with PEN faults,
but that's just me, I don't like TN-C-S very much as an earthing arrangement as a few people on here would probably tell you.
 
and it looks like he's gone back to sleep for another year,
 

Reply to Plug & Play hot tub installation in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
658
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
729
I am using a 160watt-200watt multi uv tube stand alone sunbed,When the 2 power leads (plugs protected by 2x13amp fuses) plugged into a double wall...
Replies
9
Views
769
Hi, just helping someone out and apologies for the long winded post. Would like install a couple of weatherproof double sockets on the patio. 1...
Replies
3
Views
761

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock